Hi

I have been tasked with installing a MVI46-MCM into a SLC 500 system. I have never done this before and would like to know how to copy Floating Point and Digital Signals into the Module itself. I understand how it works for integers using the sample logic that come with the card but need a bit more clarity on how to copy the rest.

Any help would be great
 
It's hard without more clarity on what you mean by copying the data into the module. From the PLC or from external modbus devices and if you are using the module as slave or master. Project 101, like any other engineering problems, in other word.

Let's start from what you know. By now I assume you know what modbus device(s) you are going to talk to. Usually, you have no choice if these devices are slave or master and typically they would be slave devices. Give us a quick description or diagram of the communication scheme. You will also need basic working knowledge of modbus which you can learn readily on the internet.

With most Prosoft module, the module holds internal database made us integers. In Prosoft setup you then assign these integer to be modbus addresses and also PLC addresses. So for example, an internal module address of 100 can be assigned as modbus register 4000 and PLC address [300].

So Internal[100] = Modbus 4000 = PLC [300], so anything you MOVd or COPy into PLC[300] will become Modbus [4000] and vice versa.

The above works once you added the ladder logic as provided by Prosoft and also configured the Prosoft internal commands and setting with PCB (Prosoft Configuration Builder).

<note that I'm just giving an example of how database of a Prosoft module is handled and I haven't touched modbus in a while, actual address correspondence depend on your assignment>

When working with Prosoft it's best to keep a spreadsheet of how you set up the addresses and commands to keep everything straight. Prosoft also got great free phone support and they can walk through for you step by step if needed be.
 

Similar Topics

Hi All, I am trouble understanding how the Modbus card addresses are configured with respect to slave device addresses. SLC500 is running the...
Replies
0
Views
1,614
Hello all, I have a problem to go RUN mode for my PLC. I am using 1747-L532E controller. It has turned to major fault (error code = 15Ch) when I...
Replies
9
Views
3,319
Hello all, We are currently developing a multiphase metering system that will be based on a Micromotion Altus NOC and Allen-Bradley SLC-5/04 PLC...
Replies
0
Views
4,442
Has anyone here attempted to connect Ignition to a SLC with a Prosoft MVI46-DFNT? I am able to do read/writes to the card from a compactlogix but...
Replies
3
Views
1,465
I have some equipment with Allen Bradley SLC 504 PLC's, that have a Prosoft MVI46 ethernet module installed. I would like to configure it to talk...
Replies
1
Views
3,154
Back
Top Bottom