Need help on LogixPro bottle sim.

Jonny Rev

Guest
J
I'm struggling to find a way to get the large bottles to fall onto the second conveyor,,, If somebody could help me get started. This electrician would be very greatful!!!
 
Use B3:5/4 bit. since B3:4 file length is 32 bit card and binary table is only 0-15 bits u have to use the next file B3:5/4 is the right bit target to open the solenoid
 
Yes, specially because the correct bits to use for the Large Bottle Diverter in Exercises 1 to 5 using BSLs are: XIC O:2/10 AND XIC I:1/6 AND XIC B3:5/5 AND XIO B3:7/3. For exercise 6 using BSRs, the bits should be: XIC O:2/10 AND XIC I:1/6 AND XIC B3:4/10 AND XIO B3:6/10.

O:2/10 = System Run Indicator (no Output should be able to energize if not in RUN mode)
I:1/6 = Encoder pulse "LS1 Exists'
B3:5/5 = Large Bottle sitting on the Diverter Gate
B3:7/3 = Broken Bottle bit at the Diverter Gate. If a broken bottle was previously ejected, leaving a space, then the Diverter should not be energized (causing unnecessary wear).
 
Last edited:

Similar Topics

I'm using loxixpro. My problem: I enter an RTO but cannot put an address to it. I have tried every way I can think of.
Replies
4
Views
1,761
Greetings, I have been using LogixPro program and i am really bad with it..:bawling: I am working on Bottle Line and got lots of problems.. i...
Replies
2
Views
1,829
I was wondering if anyone could help i am trying to use a SLC 500 with a 5/05 processor to set up an incremental encoder to a HSCE2 card? The card...
Replies
2
Views
199
I have an old Sentry Palletizer (S/O Number 3007 / Serial Number 1172) that has lost its program as the backup battery died years ago. I can...
Replies
0
Views
179
So i've been at this for a long while, i have Citect Scada 2018, i have full access to everything but i can't seem to find any option or...
Replies
0
Views
138
Back
Top Bottom