network parameter setting problem (CC-Link)

icekalt

Member
Join Date
Mar 2011
Location
Selangor
Posts
10
Currently I'm using CC-Link modul QJ1BT11N as master station. The CPU I'm using is Q Series CPU, Q02(H). The problem is, I don't understand how to set the parameter value of remote register RWr and RWw. The original and correct network parameter setting shows

all connect count = 22
RWr = D12000
RWw = D12100

Because I want to add more stations,
I changed all connect count to 29. Then an error is shown:

The refresh device settings are overlapping. Please take care that the device settings do not overlap.


When I changed RWr = W0 and RWw= W1000, with all connect count = 29, there is no error.

Can I simply changed the RWr and RWw to W0 and W1000 respectively? Does it have any effect on my program?

Thanx in advanced

network parameter setting.jpg
 

Similar Topics

I have a A3A mitsubishi cpu plc master and local connecting through coxial cable , these two plcs exist in printing machine and the master one...
Replies
0
Views
1,278
Hi All, I need some help here, I'm trying to set up this CP5512 adapter to communicate with the Siemens PLC, all I left is to set up the...
Replies
4
Views
3,797
Hello, I have a A.B Compact logix communicating with two fanuc robots via ethernet. The plc also communicates to an automation direct hmi screen...
Replies
3
Views
143
So I'm pretty new around here but I come looking for advice or suggestions to research. Im the plant electrician/SCADA guy for a warer department...
Replies
8
Views
209
Looking for a supplier of Layer 3 Network Switches DIN RAIL MOUNT, in Alabama, In the UK we would use Typically in the UK we would use...
Replies
6
Views
178
Back
Top Bottom