BUMP;
I decided to resurrect this thread because I think it's important and I had to deal with this again today. The posts made by Lancie, DickDV, Jiri, and Leadfoot are all worth reading again for anyone who has to deal with drives and power systems.
I got called first thing this morning to a drive that had an overvoltage fault that would not clear. Checked phase - phase and all three are OK. Start checking phase to ground and the voltages are all over the place.
Sure enough we had a phase go to ground at the PDC and the ground fault annunciator was blinking as bright as it could in a room nobody ever enters. Spent most of the day tracking down and fixing the ground fault. I know where I work these annunciators are checked only randomly when someone happens to be in the room. How long it was there I don't know.
I spent the latter part of my day trying to explain this to some of the other plant management (some technical some not) my recommendation of switching to a hard grounded system. I remembered this thread and printed it out for them, hopefully they will read it tonight.
Any additional insight from those in the know would be appreciated.
EDIT:
The tx I was working on was a wye secondary 3MVA high resistive ground.
I decided to resurrect this thread because I think it's important and I had to deal with this again today. The posts made by Lancie, DickDV, Jiri, and Leadfoot are all worth reading again for anyone who has to deal with drives and power systems.
I got called first thing this morning to a drive that had an overvoltage fault that would not clear. Checked phase - phase and all three are OK. Start checking phase to ground and the voltages are all over the place.
Sure enough we had a phase go to ground at the PDC and the ground fault annunciator was blinking as bright as it could in a room nobody ever enters. Spent most of the day tracking down and fixing the ground fault. I know where I work these annunciators are checked only randomly when someone happens to be in the room. How long it was there I don't know.
I spent the latter part of my day trying to explain this to some of the other plant management (some technical some not) my recommendation of switching to a hard grounded system. I remembered this thread and printed it out for them, hopefully they will read it tonight.
Any additional insight from those in the know would be appreciated.
EDIT:
The tx I was working on was a wye secondary 3MVA high resistive ground.