Our customer has a site with 3 SLC 5/03 PLC's, one main PLC that gathers 7 AI from the two others via radio (no cable possible since on a rotating reactor).
One of the "slaves" has started blinking on the fault LED, we have tried to switch the CPUs and the fault followed the CPU. When I got RSLinks to communicate with the CPU it has an error.
"Error code = 0001h, Default program loaded due to NVRAM error. A corrupt CRC was detected (loss of battery power may cause this), or a power cycle in the middle of a user program download, initialize memory. or memory module load. Cannot go online or upload from DEFAULT processor (no program). You must perform download."
Since these PLC's are some years we have decided to change the batteries. Is it possible that faulty battery is the cause for this?
When we tried to connect to the other "slave" we don't get any response. Using RS232 DF1, SLC-CH0/Micro/PanelView and everything else is just as the other "slave". What can be the problem? This PLC is working and no error.
I am no AB expert, only helping our customer that have some old AB PLC's. I am also not on site, I do all remotely and sends the local operator over her and there to connect or disconnect cables.
One of the "slaves" has started blinking on the fault LED, we have tried to switch the CPUs and the fault followed the CPU. When I got RSLinks to communicate with the CPU it has an error.
"Error code = 0001h, Default program loaded due to NVRAM error. A corrupt CRC was detected (loss of battery power may cause this), or a power cycle in the middle of a user program download, initialize memory. or memory module load. Cannot go online or upload from DEFAULT processor (no program). You must perform download."
Since these PLC's are some years we have decided to change the batteries. Is it possible that faulty battery is the cause for this?
When we tried to connect to the other "slave" we don't get any response. Using RS232 DF1, SLC-CH0/Micro/PanelView and everything else is just as the other "slave". What can be the problem? This PLC is working and no error.
I am no AB expert, only helping our customer that have some old AB PLC's. I am also not on site, I do all remotely and sends the local operator over her and there to connect or disconnect cables.