NT21-ST121-E and CQM1H-CPU51 connection
DavidNelly
Jan 2008
JURONG
Dear colleagues,
I am very new in PLCs and automation.
Now, I got a problem. When program in PT is accidentally erased by operator, I copied from the same machine and connected to the PLC ( CQM1H-CPU51). Now, the PT screen is stoped in program's first screen. Any connection setup for PT and Host PLC ?
I found in PLC program that host port is in host link.
Need to set up the same in PT ?
Thanks in advance.
Yes, the PT communications setup needs to be the same as the PLC port setup. Check the communication setting in the Memory Switch menu of the Maintenance mode, and match the communication protocol settings for the host and NT21.
How did you "copy" the application? With a memory unit or NT Support Tool? Did you check the setting of the PT Control and Notify area?
Thank you, P.d.L,
I copied with NT support tools.
I can see the following from PT configuration:
PT Control area:
PLC address:
H00000
PT Notify area:
PLC address:
H00010
Window control area:
PLC address:
H00090
Is it useful for settings ? Hope to hear from you, please.
Have you done this ?
Check your PLC program if there is any reference to Holding Relay words 0 through 3, and if there is, if it is used to control the NT21.
So I understand the first screen of your application just "freezes" in other words you cannot open another screen by a screen switch button, but you do not get a host connection failure either?
Do the comms LED on the PLC Host Link port flicker?
It could be H0 is set to a value (in this case the current screen no in BCD) constantly, you should verify this in the program.
Hope this helps.
Thank again, P.d.L,
Your informations are very helpful.
Tomorrow,I'll do all what you suggested me.
Then I'll inform you. I attach screen capture of HR0 area usage. I am not sure you asked me for H0 is related to attached image.
Thanks again. Hope to hear from you,please.
Thank you very very much!! , P.d.L,
I checked in memory switch menu of maintenance mode,there was set in NT link mode, then I changed to Host link mode and this time, everything is ok.
I appreciate and thank you for your help.
See you
I have a customer that bought a used machine (was told it was working) it has a C200HS omron cpu31 and a NT21, when he plugs in the cable there is...
138
I was called out to a site today that I had never been to before. They have an Omron CS1G-CPU43H that was communicating to a NT21-ST121B-E HMI via...
1,452
Please, I have more option as the pic is showing to download to PT Which one to choose " Application" only or All ??
1,317
Dears I wonder if I can work and navigate on my Omron HMI NT21 through pages without connecting to the PLC because it sticks/freezes on "System...
2,024
I have to make a small change to an Omron NT21 HMI at a remote site. I have remote connection to the CJ1M PLC the HMI is connected to through a...
3,128