Omron issues NT21 and CPU31

geniusintraining

Lifetime Supporting Member + Moderator
Join Date
Jun 2005
Location
SC
Posts
8,277
I have a customer that bought a used machine (was told it was working) it has a C200HS omron cpu31 and a NT21, when he plugs in the cable there is an error on the HMI he made a new cable thinking that maybe it was a cable issue but it did not help, he bought a cable from me to try and upload the program from the PLC but they can not connect to the PLC either, there are some dip switches on the PLC any chance that the switches are in the wrong settings? he is using a trial software from Omron

See attached PICs on the errors, is there a way to see the COM settings on the HMI?

As always... thanks for the help
 

Attachments

  • image3.jpeg
    image3.jpeg
    68.4 KB · Views: 14
  • image2.jpeg
    image2.jpeg
    63 KB · Views: 15
  • image1.jpeg
    image1.jpeg
    72.3 KB · Views: 14
  • image0.jpeg
    image0.jpeg
    71.1 KB · Views: 14
Here's a link to the manual V068-E1-01 page 118 will explain getting into installer mode etc. You will be able to find the comms setup of the NT in the maintenance mode menu.
 
Mark,
Possibly. Dip Switch 5 switches between the default when ON.
It will use the programmed settings when OFF.
Need to know how Port A on the NT is configured.
Should be able to hold down opposite corners on the screen to access the menu.
Turning dip switch 5 to on should allow them to connect with CX Programmer with network type Host Link (Sysmac Way).

What cable did he buy?
USB-CIF02 would connect USB to the peripheral port.
C200HS-CN220-EU (USB-GTC99CC) would connect to the 9 pin port on the cpu and also the NT21.

1708542288812.png
 
Thank you both very much, I have passed on the information and hope it solves his issues
 
Success!!! Below is from my customer, thanks again

Mark I wanted to share that I was able to connect and configure the port with both the replies on the forum. It was the dip switch 5 and the manual for the NT21 brought me to the Maint screen to configure. Thanks again! Super helpful!
 

Similar Topics

Hello ! I am trying to use an omron cj2m-cpu33 with a CP1W-CIF01 plug in serial connector to talk to a zebra ZT610 printer. I am getting the data...
Replies
8
Views
381
Hello all, I'm new to the Sysmac Studio software and I'm having an issue with the HMI screens crashing. I have a screen that shows the active...
Replies
1
Views
1,974
Good Afternoon guys, I have a good one today. Have a NJ101-9020 CPU, a NX safety PLC, a NA5-7W001 HMI and finally a ABB 910SC SCARA to...
Replies
0
Views
1,212
I'm trying to connect an Omron HMI and Omron PLC together for a trainer at work. I have a program in both the PLC and the HMI. On the HMI I have a...
Replies
3
Views
4,662
I am trying to connect my 7" Omron NB7W-TW00B HMI to my AB CompactLogix L-31 PLC. Right now I am just trying to pass a single value from my PLC...
Replies
1
Views
3,924
Back
Top Bottom