Paulus said:
Hello Khirad,
When the instruction dialogue appears, type in either sys or 49.
This will then change to SYS(49).
I don't have a problem with this when using Syswin 3.41.
The block checks OK.
FUN49 is the equivilant instruction in CX-Programmer (I'd recommend upgrading!).
If you have any more info, then please let me know, and I'll try to delve deeper.
Dear Mr. Paulus
Many thanks for your response. I tried all the ways, but no success. Probably my Syswin 3.4 needs to be updated. I have noted that CQM1H is not included in "Availability" section of Set System Sys(49) command. I have coppied below the details from reference section of SYS(49) instruction.
Regards
Khirad
:Quote
SYS(49) - Set System
Differentiated variant available.
Purpose:
SYS(49) is used to control the following 4 operating parameters:
1. The battery check in system error checks. If SYS(49) is executed and bit 00 of OPR1 is ON, the
battery check will be excluded from system error checks when PLC power is turned ON.
2. The initial operating mode. If SYS(49) is executed and bit 01 of OPR1 is ON, the PLC will enter
MONITOR mode when PLC power is turned ON (see Initial Operating Mode below).
3. The Force Status Hold Bit (SR 25211). If SYS(49) is executed and bit 06 of OPR1 is ON, the
Force Status Hold Bit (SR 25211) will be effective when PLC power is turned ON.
4. The I/O Status Hold Bit (SR 25212). If SYS(49) is executed and bit 07 of OPR1 is ON, the I/O
Status Hold Bit (SR 25212) will be effective when PLC power is turned ON.
Ranges:
OPR1 Parameters # nnnn or 0 (IR0)
OPR2 Online switch # nnnn or 0 (IR0)
OPR3 Password # nnnn or 0 (IR0)
Availability:
CxxH, C200H, C200HS, C1000H, C2000H, CPM1, CQM1, IDSC and C200HX Family.
: Unquote