Hi there,
I’m not sure how familiar most of you are with Wago remote I/O, but I hope you may have some solution for the following connection problem I’m having.
I’m working on a project to modernise an old folder collecting machine for which I’m using an Omron CJ2M Cpu33 together with 8 Wago 750-352 remote I/O units over ethernet/ip.
These Wago units all contain two 8DI digital input cards and two 8DO digital output cards alongside a 750-610 bus power supply card.
Adding them to my network in CX network manager is no problem and all seems to work fine. That is, as long as I don’t physically add the bus power supply card, which I need to, well.. power the Wago bus.
Soon as I add this card (which was in place while making all the necessary settings to the Wago and Omron units) it just won’t connect. Remove it and it connects like it should.
As far as I know the power supply card has no I/O addresses or other communication functions whatsoever, so I can’t get my head around it.
Even stranger is that when instead of it I add an analog input card, with bus power connections build in, it connects without a problem.
The .eds file only contains info about the main Wago unit, after installing it I should be able to add any kind of I/O card and address them in the Omron software.
Also, the supply card is added and visible as a fifth card in the Wago I/O settings and the I/O status led is green during this error. Therefore I would say the problem is at the Omron side.
Any sugestions?
Thanks in advance
Andy - The Netherlands
Hello Andy
According to the manual the 750-610 provides Some statusbits. I used 750-602 module with 750-352 coupler configured as modbus tcp server to Exchange I/0 with a Unitronics plc. The 750-602 is passieve and has no statusbits, means that no additional configuration is needed. I have no experience with the 750-352 as ethernet ip adapter. But for me this sounds like a configuration problem where in your new setup the diagnostic is perhaps enabled and in the old situation not?
My advice would be to contact Wago Netherlands in Apeldoorn and ask for mr Top or mr Maneschijn. I have very good experience with their support.
Kind regards
Henny
Hi Henny,
I figured I’d have a much bigger chance of someone having a solution when asking on an American forum, since it’s backed by a lot more people.
Still it’s a fellow Dutchman comming up with an answer :)
I checked and you’re right. Didn’t realise this card provides a status bit.
I’ll see if I can find a workaround, and will contact Wago if I have to. Otherwise I’ll just order the 750-602, since it’s just 13 Euros a piece.
Thanks for your reply!
Thanks!
I’ve been thinking, this statusbit is a single bit which makes it an uneven one?
The omron doesn’t accept uneven bit counts.
Now there’s an option in the Wago coupler to make all bits even, which is set, perhaps that’s not possible with this single status bit.
I might be completely wrong here but it’s something I can ask the Wago technicians tomorrow.
The solution was buying passive supply cards. There’s no way to even the status bits, Wago confirmed.
Case closed:beerchug:
Has anyone done SMS messaging from an Omron CJ2J-CPU31 PLC? If so could you help please. Omron here in Oz have not had any experience doing this...
174
I have an old plc in the system I have, moxa nport was used to communicate with scada, I want to replace the plc with cj2m cpu33 and eliminate...
64
Hi all, i have 8 CJ2m plc units that show different numbers on the plc display and i am stuck on reading the info. my unit has an ip address of...
108
I have PLC Omron CJ2M with OD211 module. I want to use the pulse output and PWM output and this module. But i confuse how to activated this, i...
117
I have a project to control the speed of motor DC using PWM Output on PLC and when im on working i have a several trouble and of of them is the...
225