Omron CPM1A-MAD01 Help
Jayden
Dec 2007
camperdown
41
Hi all. I am Currently trying to learn Omron programming using CX programmer 6.11. I have a CPM2A Processor and a CPM1A-MAD01 analogue card. Can someone please step me through how to install the analogue card. I thought there would be an I/O setup in the project menu on the left of screen but I cannot find anything.
The CPM2A PLC using CXProgrammer is not as straight forward as you might think. Access to an expansion module is done entirely via the program. If you are using a single expansion module, the addressing is done using the formulas as follows.
Input 1 = (M + 1)
Input 2 = (M + 2) Where M is the last input number allocated to the processor.
Output 1 = (N + 1) Where N is the last output number allocated to the processor.
I strongly recommend you download the CPM1/CPM1A/CPM2A/CPM2C/SRM programming manual from Omron's website. Section three of the manual is called Using Expansion Modules and describes all the setup requirements for the MAD01 analog module.
I have a Omron PLC with CPM1A-MAD01 anaolog input output module its reading pt100 temperature probe. When the machine is running it starts to...
1,102
I've got an upload from an Omron SYSMAC CPM1A PLC but I cannot figure out for the life of me how to document the inputs and outputs. It's version...
3,310
Hi, I have recently purchased an old Omron Cpm1a plc to practice on. I have a version of syswin that does not require a licence to program these...
1,675
Hi, I have recently being using a Omron CPM1A-40CDR-D-V1 and transferred an old program on it. I was testing the program and making some...
4,266
I have two of the same units that are using a CPM1A and an NT20S-ST121B-EV3. I am not able to connect to the touch screen as far as i can tell via...
4,016