Omron CQM1-TC002, which addresses?
The_Harlequin
Feb 2011
Europe
30
Hey!
I have problem with a thermo-card (CQM1-TC002).
I have a CQM1CPU and the thermo-card connected.
The unit have 2 thermo inputs and 2 PNP-transistor outputs. I have get the inputs, the inputs addresses were 1 and 2, because it's 16 internal inputs in the CPU.
But, what is the outputs addresses? I have test 100.00 ->.
Thanks in advance!
This is not an easy question to answer.
Typically the output is controlled by the module.
You enter the loop setpoint to the output word and the module controls the output as required to control the temperature.
I would suggest you take a look at the W238 manual.
This is the Special I/O module manual for the CQM1.
There is a section in this manual that should answer your questions.
Hope this will help.
If the adress of the TC002 is 0, then the 1st two setpoint words will be 2000 and 2001. The two output status bits will be 2008.04 and 2009.04. The two process words will be 2003 and 2004.
I agree with gtsuport .... read the manual.
Ahaa, so it isn't possible to set the outputs manually in the TOGGLE WATCH WINDOW in CX PROGRAMMER... ?
Soon I will read that manual =) Thanks for the tips...
EDIT: I have now read about it. What I can understand, this is a thermo-control module. I must set a setpoint of the inputs, and if for an example, the temperature goes over this setpoint, then a output will be set? It's like alarm-outputs?
This is not correct. The Output bits are not alarms. They are indication bits to show if the output from the controller is active or inactive.
For the alarms you need to set the alarm threshold and use a comparator in your PLC program to set a fan output ect.
Hi! Has someone a pinout and/or wiring diagram for an old CQM1-CIF02 cable? Thanks!
1,904
Hi; I have a DUPONT brand machine having OMRON PLC CQM1-CPU21-E. I have CX Programmer installed in my Laptop having W1indow10. I want to go...
3,607
Dear All, Does anybody knows Omron CQM1 0ch Module details?? or manual i try to search but cant find manual or complete order code if this...
2,366
Hi, I've been asked what is involved to upgrade and old CQM1-21 Omron PLC to a CJ2M. I have the old file with an extension of .cdm and searches...
1,586
Hi Everybody I have a very old CQM1 CPU21 Without memory cassette. I´m trying to set up protection UM, but I can´t, the following warning "Error...
3,308