Omron CS1GH-43 CPU Communication Problems
ejones76
Sep 2005
SC
Hello All,
I am new here so please bare with me. I have an Omron CS1GH-43 CPU along with an internal CS1W-SCB41-V1 ver. 1.3 comm board setup. I have a simple Protocal macro setup for this board. Using PMCR instruction in plc ladder logic. When I force the rung true with the PMCR instruction, I believe if everything is setup correctly the COMM1 light on the serial board should flash, weather a cable is connected to it or not. Right now the light isn't flashing so I am not getting any communications. I have checked and double checked the setup for the serial board and everything seems correct. Am I correct when I say the COMM1 light should be flashing when the rung goes true with the PMCR instruction? Sorry for the long write but can't figure this one out.
Comm light may or may not flash. It will depend on the CTS/RTS settings. If CTS/RTS handshaking is enabled, you would need a signal on the RTS line. Easiest way to check this is to jumper pins 4 and 5 on the port.
Hope this helps.
I would double your settings again. Have you loaded a file with cx-protocol? Does the PMCR executing bit come on?
Here's an example of a PMCR with the SCB
This will use Port 1 (F1 part of F1E1) and macro number zero.
The address of the 'executing' flag is 1909.15
I think you need something connected (Data carrier detect??)
Pp
Hi guys, I can't try communicating Omron CS1GH PLC to Kepware.:banghead: I'm using port 2(RS-422/RS-485) of the SCB-41 internal board. I tried...
1,985
Has anyone done SMS messaging from an Omron CJ2J-CPU31 PLC? If so could you help please. Omron here in Oz have not had any experience doing this...
145
I have an old plc in the system I have, moxa nport was used to communicate with scada, I want to replace the plc with cj2m cpu33 and eliminate...
63
Hi all, i have 8 CJ2m plc units that show different numbers on the plc display and i am stuck on reading the info. my unit has an ip address of...
102
Hi all, Currently having trouble getting a speed reference to write over modbus to an Omron M1... I can successfully write a run command and...
256