Hi guys,
I can't try communicating Omron CS1GH PLC to Kepware.o_O
I'm using port 2(RS-422/RS-485) of the SCB-41 internal board.
I tried using the drivers FINSSERIAL and OMRON TOOLBUS.
I'm sure that my cable wiring is correct.
Have anyone tried this before?
I appreciate your ideas. Thank you
Cannot help I am afraid as I do not use serial or confounded OPC but native drivers always. You should always run 4 wire RS422 though - I have done that successfully serially to Citect but used the inbuilt Citect FINS driver not OPC.
which version of kepware are you using?
Try using 4.6
setup the channel
then select either the FINS or toolbus (wife just spoke to me might have been host link sorry)
Both of these have the CS1 selection
you will need to move forward from there.
There are several reasons why you may not be communicating.
1. You could be trying to use a driver that does not match how the device is configured to communicate on that Port. Have you verified how the communications port is configured and for what protocol.
2. The wiring diagram Kepware provides is for the RS232 port so it should not be used for port 2
3. For the Fins protocol you need to know the Hostlink ID for the PC interface typically 0, its Fins Network address and the Fins destination node number. This can be acquired from the CX Programmer software when the device is configured. Toolbus addressing is similar to the fins addressing. However the numbers have to match.
If all else fails you can contact Kepware Tech Support.
Hello All, I am new here so please bare with me. I have an Omron CS1GH-43 CPU along with an internal CS1W-SCB41-V1 ver. 1.3 comm board setup. I...
3,548
Has anyone done SMS messaging from an Omron CJ2J-CPU31 PLC? If so could you help please. Omron here in Oz have not had any experience doing this...
144
I have an old plc in the system I have, moxa nport was used to communicate with scada, I want to replace the plc with cj2m cpu33 and eliminate...
63
Hi all, i have 8 CJ2m plc units that show different numbers on the plc display and i am stuck on reading the info. my unit has an ip address of...
102
Hi all, Currently having trouble getting a speed reference to write over modbus to an Omron M1... I can successfully write a run command and...
256