Omron Memory Map Help
PaperMan
Jul 2007
Weeton
Hi All,
New to Omron, looks straight forward (usually I do Siemens and AB) apart from one simple thing, for the life of me I cannot find any information regarding all their different memory areas. CI0, HR, AR, LR, DM, WR, EM, EM and Extended EM. Lots of help on the instructions etc but this basic information seems to have been overlooked.
CPU is a CJ1G-CPU45
Any Help – especially a link to a pdf would be most appreciated (already downloaded over 20 without result)
Thanks in advanced
PaperMan,
Download the W339 manual. There will be an entire section on the Memory Map. This should answer your questions.
Quick Answer:
CIO - Actual I/O point (unused can be internals)
HR - Holding Relay Area - maintains status thru power failure
AR - Auxillary Relay Area - mostly Status information
LR - Link Relay Area - used for PLC to PLC data xfer
DM (D) - Data Memory - Internal Data Storage Locations
WR (W) - Work Area - Internal Bits
EM - Extended Memory - Additional D type memory
Hope this will help.
Hello PaperMan,
Just to add to gt's help...
CIO (no need to prefix with CIO, just use the numbers) - Word and Bit addressable.
HR (prefix H) - Word and Bit addressable
AR (prefix A) - Word and Bit addressable (A0 - A447 Read Only)
LR - Not available for CS / CJ series
WR (prefix W) - Word and Bit addressable
DM (prefix D) - Word addressable only
EM (prefix E) - Word addressable only
On your CPU type, there are 3 banks of E (E0, E1, E3 - addressed as E3_100 for example)
Hope this helps.
Paulus said:
Hello PaperMan,
HR (prefix H) - Word and Bit addressable.
DM (prefix D) - Word addressable. Bit addressable using instructions TST[350],TSTN[351],SETB[532] and RSETB[533].
EM (prefix E) - Word addressable.
Hope this helps.
BITS N BYTES said:
Hello BITS N BYTES,
Time for the gloves to come off... ;)
OK, instructions can determine / set the status of D and E 'bits'.
What I meant however is, they are not freely addressable (i.e. LD D0.00 OUT E0_12.2) within a ladder program for example.
(Believe it or not, there is absolutely no reason why this should still be the case with the CS / CJ / CP range o_O )
Hi Paulus,
I understand exactly what YOU meant.
BUT the original poster is a newbie to OMRON, I was simply clarifying that D and E memory can be accessed at both a WORD and BIT level.
Your statement "Word addressable only" could be misleading to those unfamiliar with OMRON.
Hello, I want to understand the memory mapping of a CPE1 Omron PLC. Which areas are accessible and generally operate like a flag bit. Second...
2,146
Project involves updating a ~23 year old controller (C200HX CPU64). The HMI is a windows NT machine with the gui done with Delphi 5 (Pascal)...
1,131
Hi All, I'm going to start with that I'm new to Omron and this is the first time I'm dealing with an Omron PLC. I have a project...
1,988
Hi All, I have an Omron PLC program which is copied from the memory card. Could you please tell can I open the PLC program using CX programmer or...
969
Hi everybody. On omron plc cpu20 ihave constant memory err After bettery drain and plc got out of power i removed all errors with pro15 but i cant...
1,189