Hi.
For a project I’m programming a 10 inch Omron NB hmi. Now, creating an event or alarm screen is no problem, however all event related screens have the same small font.
I want to decide myself how I review ongoing events, in this case I want a bigger font and different color.
Any ideas?
Thanks,
You can change the font in the alarm property dialog box.
NB-Series-Programmable-Terminals-NB-Designer-Operation-Manual.pdf
Thanks man, I was looking For settings in the event/alarm screens. It didn’t occur to me that I can change the font in the actual event list.
Thanks again, case closed.