yoursalmann
Member
Hardware:
CS1G-44H CPU (With memory card)Omron
NS10 PT (with memory card)Omron
CS1W-SCB41 board, (RS232/422 used).
CS1W-MAD44 (Analogue I/O)
Problems:
.
Task . PT showing “connecting” message on the right down corner.
(According to V083-E1 page 3-9 this happens when PT is connected using communications conditions other than the set conditions)
Present settings:
Plc settings:
Host link port: communication settings
(Standard 9600)Mode: host link
Peripheral port: communication settings
(Standard 9600)Mode: host link
PT settings:
Should be (serial PortA: PLC; protocol:NT link (1:N))
baud rate: standarrd
Solution: kindly guide me are these correct solutions??
As the system was working ok before removing plc memory card so the solution could be:
a).
This means no change could happen to communication settings in PT (please note memory card is present).
so should I change (see below)
Host link port settings as below and transfer it to (plc? Or memory card?) :
new Changed settings?:
1. Host link port: communication settings
(Baud rate as per PT settings)Mode: NT link (1:N)
(PT setting check as per V083-E1 page 6-7 and 6-35,4-20)
W394E106 page 284 for plc
any other suggestion????/
CS1G-44H CPU (With memory card)Omron
NS10 PT (with memory card)Omron
CS1W-SCB41 board, (RS232/422 used).
CS1W-MAD44 (Analogue I/O)
Problems:
.
Task . PT showing “connecting” message on the right down corner.
(According to V083-E1 page 3-9 this happens when PT is connected using communications conditions other than the set conditions)
Present settings:
Plc settings:
Host link port: communication settings
(Standard 9600)Mode: host link
Peripheral port: communication settings
(Standard 9600)Mode: host link
PT settings:
Should be (serial PortA: PLC; protocol:NT link (1:N))
baud rate: standarrd
Solution: kindly guide me are these correct solutions??
As the system was working ok before removing plc memory card so the solution could be:
a).
This means no change could happen to communication settings in PT (please note memory card is present).
so should I change (see below)
Host link port settings as below and transfer it to (plc? Or memory card?) :
new Changed settings?:
1. Host link port: communication settings
(Baud rate as per PT settings)Mode: NT link (1:N)
(PT setting check as per V083-E1 page 6-7 and 6-35,4-20)
W394E106 page 284 for plc
any other suggestion????/