Omron v1000 drive wiring braking resistor

unsaint32

Member
Join Date
Oct 2012
Location
minneapolis
Posts
365
The B1 and B2 terminals are for thermal relay AND for braking resistor. Doesn't this mean if the thermal relay trips I have no dynamic braking? I just don't see the advantage of this wiring configuration.

omron v1000 wiring.jpg
 
They want you to install a fuse to keep the resistors(and other things) from catching on fire. Yes, you will lose dynamic braking at that point and the drive should trip on high DC bus voltage when it tries to brake and it needs the resistors.
 
Last edited:
That's not a motor or drive thermal switch but one mounted in the brake resistor housing. If the brake resistor has been sized too small or the braking energy is unexpectedly too high or if the cooling air is somehow cut off to the resistors, then the switch will open and save the resistors or prevent a fire.
 

Similar Topics

the parameter is for motor rated current. The range is 10 - 200% of drive rated current. But the actual value is displayed something like 0.8...
Replies
2
Views
1,685
HI; i have in stock PV1000 DH+ ,and i want install this PV with OMRON plc CS1J CPU44; is there possible ? if is ok ;please descript a...
Replies
8
Views
2,766
Has anyone done SMS messaging from an Omron CJ2J-CPU31 PLC? If so could you help please. Omron here in Oz have not had any experience doing this...
Replies
5
Views
138
I have an old plc in the system I have, moxa nport was used to communicate with scada, I want to replace the plc with cj2m cpu33 and eliminate...
Replies
1
Views
63
Hi all, i have 8 CJ2m plc units that show different numbers on the plc display and i am stuck on reading the info. my unit has an ip address of...
Replies
3
Views
100
Back
Top Bottom