Omron's MOVD (read with caution)
theripley
Jul 2008
laguna
545
CAUTION: This will be a long post.
I get a little confuse with MOVD (MOVE Digit) instruction of omron PLC.
According to an explanation I googled, a MOVD instruction has 3 elements: Source (S), Control word (C), Destination (D). The Source (S) is the value to be copied, control word (C) is the manipulator of the "movement", destination (D) is the destination of the copied value starting from the digit specified in C and filling in to the left.
Example:
MOVD DM0 #0132 DM10, DM0 = 5678 (D3=5, D2=6, D1=7, D0=8)
S = DM0
D = DM10
C = 0132 (D3=0, D2=1, D1=3, D0=2)
D0 = 2 (Specifies the 1st digit copied from source, the value must be
from 0 - 3)
Hence, the D2 of DM0, which 6, will be the first to be transferred
to the location specified by D2 of C.
D1 = 3 (Indicates the number of digits to be copied, 0=1 digit, 1=2
digits, 2=3 digits, 3=4 digits)
Since D1 of C = 3, hence we will move all 4 digits of Source to
Destination.
D2 = 1 (Indicates the starting digit that the data will be moved into
the Destination)
The D2 of DM0, which is 6, will be moved to D1 of the
Destination. The rest of the digit will be copied in the same pattern and
wrapping back around to D0.
D3 = 0 (The MSB must always be zero)
Hence result of the "movement" will be:
MOVD DM0 #0132 DM10 (DM0 = 5678, DM10 = 8567)
Continue to next post.........
If I have:
MOVD DM0 #0000 101, DM0 = 3 (D3=0, D2=0, D1=0, D0=3)
Hence,
101 = 3
102 = 0
103 = 0
104 = 0
However, 101 is a bit. So how it is going to function having a value of 3?
I see.
Hence,
D0 = 101.00-101.03
D1 = 101.04-101.07
D2 = 101.08-101.11
D3 = 101.12-101.15
Meaning if DM0 = 3 with C = 0000, then
101.00 - 1
101.01 - 0
101.02 - 1
101.03 - 0
Has anyone done SMS messaging from an Omron CJ2J-CPU31 PLC? If so could you help please. Omron here in Oz have not had any experience doing this...
137
I have an old plc in the system I have, moxa nport was used to communicate with scada, I want to replace the plc with cj2m cpu33 and eliminate...
63
Hi all, i have 8 CJ2m plc units that show different numbers on the plc display and i am stuck on reading the info. my unit has an ip address of...
100
Hi all, Currently having trouble getting a speed reference to write over modbus to an Omron M1... I can successfully write a run command and...
255
Hi There, I have couple of Omron PLCs connected on my kepserverex and my intouch reads data from kepserverex. I have been observing that roughly...
136