OP7 Download problem

Quartz

Member
Join Date
Jan 2008
Location
Kaunas
Posts
23
Hi,
I have download problem with OP7 panel. My collegue is trying to download project from Protool (v6.0 SP2 ) to OP7. After loader is transfered
Main program starts downloading. Somwere in the middle he is getting timeout error:

Establishing the serial connection at COM 1 with 19200 baud...
Downloading Firmware...
E4026: Timeout error 1064
Download aborted with error

Its looks like cable problem, but we tried to make new one (http://www.circuitdb.com/circuits/id/66) with no luck.
He have tried change ports, speeds but again no luck.


For downloading he is using notebook with USB to COM port converter.

At the same time I have tried to download to another OP7 using similar configuration(notebook, USB-COM converter, cable) Everything goes fine for me.

I have no ideas left, what to try. Maybe you can help me
 

Similar Topics

Dear all, i tried to download a proTool project meant for OP7 onto an Op17 and the following error messages were displayed. 1, compilation aborted...
Replies
6
Views
3,420
Hello! I have problem when downloading program to OP7 for the first time. I have OP7, project compiled in protool/pro cs, 9-15 pin v.24...
Replies
13
Views
4,264
hi, i need help on this issue.i uploaded an op7 program to the pc using simatic prosave v7.3.2.0.but when i try to download to another op7 (op...
Replies
7
Views
6,555
I have converted a Siemens OP7 program to a new Delta DOP107BV. It is all working as expected except for the timer values. I am using MW36 as the...
Replies
6
Views
952
I have a customer who had a faulty Siemens OP7. They sourced a replacement. They have the original program. I downloaded the program to the...
Replies
10
Views
2,543
Back
Top Bottom