JNelson said...
"Nothing in the world drives me more crazy than looping wire back and forth multiple times in the wire duct. It makes a huge rats nest of tangled jargon that makes me irritated."
Are you suggesting that I suggested that? I recall saying something like...
"...the standard was to make a double-loop in the wire by wrapping the wire around your
thumb twice before making the termination..."
If you interpret that to mean "...looping wire back and forth multiple times..." then... I can only wonder... how fat
are your thumbs?
Then JNelson said...
"I would much rather pull in a whole new wire than deal with a mess of wires that someone has pulled out of the wireway twisted, turned, intertwined, ect. The time it takes to install a new wire is worth it to me, rather than pushing the duct cover back on with a 2x4."
Sounds to me like you are contributing to the need for the 2x4... or maybe a 4x4 by this time... no?
Then JNelson said...
"Trying to troubleshoot a panel with 300 I/O points and 1 fuse off the main control transformer makes everyone happy."
You are kidding... aren't you?
If you aren't... you don't really do troubleshooting, do you?
If you use a single fuse for outputs then that fuse has to be sized to carry the maximum load.
That means... for example... if the fuse is sized for 10-amps then that one single output transistor, or that one single 2-amp output relay, that is connected to a shorted load is going to experience... oh..., let's call it "stress". (Can you say "smoke-test" or "contact-fusing"?)
Additionally, if the single fuse blows all you know is that one of your 300 I/O has a problem.
If you are using a brick-type PLC, then, when you
finally find that particular I/O point, you might have to replace an entire module!
Yeah... after all that, I can see how one fuse makes everybody happy.
I say... if you aren't using the PLC Outputs to drive opto-isolators, fuse every single PLC Output individually! (Use indicating fuses... the kind that glow.)
Many of the larger PLCs provide a single, replaceable, on-board fuse for various numbers of actual outputs. Again, this fuse must be sized to handle maximum load... 4, or 8, or 16 outputs at a typical load of 1/4 amp each requires 1, 2, or 4-amps (plus margin). If an output is rated at 2-amps... how many times will that output suffer the pains of a blown fuse when that fuse is intended to protect the set of outputs... not just one. A 2-amp output developing 3-amps will not be protected by a 4-amp fuse.
If you are using the PLC Outputs to drive opto-isolators then fuse each opto on the source side (Again, use indicating fuses... the kind that glow.)
That... will keep everybody happy!
The dollars lost in down-time while searching for the culprit of a single blown-fuse scenario will pay for the extra hardware and construction time.
Bob,
I feel your pain. Have you considered using some of the Laws of Thermodynamics to justify a larger cabinet?
Each device in your cabinet produces a certain amount of heat. In order to dissapate the heat effectively, without resorting to fans or coolers, the cabinet needs to be of a particular volume.
I don't have the formulas... but I do seem to recall that Tom Jenkins posted them once.
Ladderlogic said...
"But I have to fit in the limited room under the machine base - period. No exceptions."
Do you remember, or have you ever heard of, "QUASAR"?
They made the first "MODULAR" TV Chassis. Maybe you could develop a way to "pull that panel" and work with it on a bench. It can't be too big if it is under the machine.
Maybe you could use an interior panel that is somewhat smaller than the box. Something like this...
+---------------------------------------+
| |
| c +-------------------------+ c |
| o | | o |
| n | | n |
| n | | n |
| e | | e |
| c | | c |
| t | | t |
| o | | o |
| r +-------------------------+ r |
| |
+---------------------------------------+
Terminate your field wiring at the "connectors". Then us a jumper-arrangement (ribbon-cable?) to connect the field terminations to the panel connectors.
When you need to work on the "stuff" you pull the ribbons, turn a few twist-locks and pull out the interior panel.
Then, in response to...
Of course, we all know that "Murphy is alive and well in every human endeavor!"
Eric said...
"Of course, this is true, but more often than not, it's the field devices that fail, since they are 'exposed'."
I totally agree that the vast majority of failures occur out in the field. And I agree with your philosophy in that respect. But you miss my point.
You, Eric, and many others, build single purpose systems. From your point of view, and reasonably so, the designs of these systems are essentially fixed... rigid.
OF COURSE, there is no reason for you to design your system for any expansion that the end-user might develop and install.
However, once in the field, in the hands of capable technicians and developers, these systems are subject to changes... that is only one of the Murphy references... as in... yeah, it's great, but what if...
But that is not where I was going. I was talking about maintaining the "innards" of the control panel. I wasn't kidding when I made the reference to wiring as if building circuit-boards. I've seen shops that run wires like violin strings... tight!
That... was my point.
paulB asked about...
"...wiring diagrams, wiring schematics, and point to point wiring diagrams..."
Depending on your definition of each of these items, each can be seen to over-lap the other.
If properly annotated, a wiring-diagram can show point-to-point physical-routings, connections, and a schematic, all in one. Of the three, the schematic is the hardest to see.
Again, if properly annotated and expanded, a point-to-point wiring diagram can show routings, connections and schematic, all in one. Again, the schematic might be hardest to see.
Wiring schematics, of course, provide the best view of the schematic. However, this method is the farthest from the actual physical layout (including routing and connection points).
When I do drawings (which I do often), I do a Schematic Drawing, a Routing Drawing and a detailed Point-to-Point Drawing. Each drawing makes references, to one degree or another, to the other drawings.
I believe that a "complete drawing set" includes each of these drawings. Each provides a particular benefit.
And since I'm the poor sot that uses these drawings, I know who to blame when they don't provide what I need.
For LARGE SYSTEMS...
As far as multiple-page drawings, I've found that the German method of coordinating the drawing and the wire-numbers works pretty well. That is, wire-numbers include schematic page number followed by wire number as depicted by particular hard-wire rung number followed by specific wire-number.
The caveat is to start Page-numbers at Page-10.
For example, wire-3 from rung-number-16, on page 14 would be wire number 141603 (that is, Page-14, really page-4, Rung-16, and wire 3.)
Of course the number scheme would have to be tailored to accommodate the maximum number of specific wires on a rung, the maximum number of specific rungs on a page, and the maximum number of pages.
This scheme accommodates 99-pages, 99-rungs-per-page, and 99-wires-per-rung. That should be enough to handle any drawing... even in size 4 font.)
If you find a wire labeled as 141603 you would go to the drawing, turn to page-14 (really page-4), look for rung-16, and find wire-3.