PanelBuilder32 Alarms HELP

busarider29

Lifetime Supporting Member
Join Date
Aug 2013
Location
Midland, MI
Posts
399
Greetings again from cold and snowy mid-Michigan.

I am trying to setup the alarms banner in PanelBuilder32. I have configured one alarm with one message so far as a test. More to come once I have this one working. I cannot seem to get the message to appear on the screen when I trigger the bit in the PLC. Can someone point me to what is probably obvious and staring me in the face but I'm just not seeing it? Alarm trigger bit is B3:10/0 if you can't see it in the pics

Thanks,
Don

Alarm Trigger.jpg

Setup.jpg

Tag Editor.jpg

Trigger.jpg

Ladder.jpg
 
I haven't done much Panelbuilder 32 but this has worked for me in the past.
In the PLC use an integer like N7:0
N7:0/0 = alarm 1
N7:0/1 = alarm 2...
Then add N7:0 to your tag editor. Then the tag to your alarm trigger, type = bit. Alarm message, Value/Bit will be 0-14 to match your corresponding bit in the plc
 

Similar Topics

Hello guys , im new at plc. i have a few questions hopefully someone can help me out. i extracted from an old panelview550 a pba file and...
Replies
12
Views
1,443
Hi guys I'll appreciate for your support. I want to know if there is a way to change the text of a label depending of the numeric value of a tag...
Replies
5
Views
1,086
I can't find what laptop I have our PanelBuilder32 application and license on. And Rockwell no longer supports it. Can someone please update 1...
Replies
5
Views
1,634
A tech at a remote facility had a PV550 **** out (Err 690 DH+ hardware failed). He took it out and sent it to me, and going by the label on the...
Replies
1
Views
1,262
I recently started getting "corrupted or low disk space" errors on all my backup panelbuilder32 files seemingly out of no where (been running ver...
Replies
2
Views
1,607
Back
Top Bottom