Panelview 1000 FTP Image Pull

Bolatov

Member
Join Date
Jun 2010
Location
Mty
Posts
87
Hello
We are using a Panelview 1000 Compact. We know it has an FPT in it.

We use a multistate indicator and in each state we selected an jpg, so it goes from 001.jpg to 099.jpg
Can the jpgs be saved in the FTP so that the MER goes take them from that path?
Thanks Guys
 
We used a ME Web Browser Control, we just put the path of our html files and put the image to fit into all the background.

But the bad thing is we cant put objects in front of it, and we need some multistate indicators to be in front of it.

Any ideas of what to do?
 
No, the images must be local to the project (PanelView).


But, you could enable the FTP server to share the Images folder on the PanelView.
Then push/upload new images to the PanelView.

You would have to overwrite existing images, already configured in the multi-state indicator (ex. 001.jpg to 099.jpg).
And, after a reboot or project restart those image changes would be lost. You would need to re-upload them.
But that does work.
 
We made it work
We connect a desktop computer to the local network where the panelviews are, just by typing the path ftp://192.168.1.xxx we could get inside the FTP of the Panelviews and put the images files in the image folder
and yes in the multistate indicator leave the pre images names

it worked great!!

Thanks a lot arlenjacobs
 

Similar Topics

Hello, I made a change in alarm setup in factory view studio, where I changed a alarm message text. After that I made a run application and...
Replies
0
Views
138
Hello brothers We are contacting you because an error like [display change is currently controlled remotely] occurred while using the equipment we...
Replies
2
Views
214
Hi All, I was wondering if it is possible to use parameter files that can be passed to a second page eg: --HOME ---PUMP 1 FACEPLATE (With...
Replies
4
Views
1,139
Hi! I recently discovered how to get to configuration mode and disable printing for connecting to PanelBuilder32 and updating my Panelview...
Replies
1
Views
452
Last night electricians replaced the panelview and now there is no comms between the panelview and the PLC. The processor is a 1747-L541 SLC 5/04...
Replies
4
Views
902
Back
Top Bottom