Panelview 1400e to controllogix via 1756-DHRIO
siv
Aug 2005
dubai
30
I am trying to connect a PV1400e terminal to a controllogix processor through a 1756-DHRIO. the problem is, in Panelbuilder 1400e the node editor does not have a device listed as controllogix. how to configure this?
Originally this was connected to a PLC-5 processor via DH+. Can I leave the node settings as it is?
thanks in advance,
Siv
Yes, you can leave the node number assigned in the Panelview project the same. However, you must then assign that node number to the DHRIO card so the Panelview can read from it. Additionally, you will need to set the tags being read by the Panelview as PLC5/SLC500 type tags. To do this click on pull down menu "Logic", Select "Map PLC5/SLC Messages", then assign the tag names.
I assume you converted a PLC5 or SLC500 project to ControlLogix.
to clarify: set the node number on the DHRIO card to whatever node number is assigned as the destination node in the PV project.
Also, don't become alarmed when the DHRIO shows the warning icon next to it. Rockwell may fix that someday. You will need to manually verify communications from the Panelview.
Attached is a screen shot from one of our convert PLC5's using DHRIO card to Panelmate (cutler hammer) via DH+
Thank you lectrofly, It was indeed a great help, it solved my issues
Thanks once again
trying to set up comms between a Controllogix PLC, DHRIO Channel A
Channel A rotary Switch set to 6
RSLOGIX5000 DHRIO Channel A set to RIO-ADAPTER
Configuration set to rack 6 full chassis
Panel View RIO configuration set to 6 full chassis last rack
Panel View Tag set to analog O:060
PLC data is shown as Rack6_1:I.Data[0] - [7]
Rack6_1:O.Data[0] - [7]
what tag in the panel view should panel view be lookig at
Hi all, I'm in the process of upgrading a PanelView1200 HMI program to be developed in FactroyTalk View Studio. The filetype for PanelView 1200...
283
Hello everybody, I am working on a project where the customer has several panelviews (PV1000e, PV1400 standard, PV1400e) which have model numbers...
1,710
I have been given the task of upgrading our (anicent) PanelView 1400e 's that we have on site, with PanelView+ (1200 or 1500). I have the *.PVD...
1,922
Panelview 1400E ser E 2711E-T14C6/E, during boot up it says "waiting firmware download from PCMCIA card or serial port". I connect from the laptop...
3,642
Hi I have an Allen BRadley Panelview 1400e 2711e-k14c6 I'm trying to load the application from another terminal [same part number] from a PCMCIA...
1,515
