Panelview 900 communication
BrandonM
Oct 2006
Prairie Du Chien
18
I am replaceing a slc 5/04 with a 5/05 so that we can hook it up to the ethernet. Currently we are using dh+ to communicate between the plc and panelview 900 which does not have a ethernet port. Is it possible to use 232 to communicate, since the 5/05 doesn't have a dh+ port. Any help would save me a lot of time from pulling a 232 cable. Thanks
yes, it will talk 232. how long of a run would it be? 232 has limitations in length while 485 will go much much farther. you may need to use 232 to 485 converters if it is too long.
It will be close to the 50 foot mark. The panelview is a 900 2711-t9c8 I tried to connect with another panelview that was the same ever time I try to changed the communications in the application setup it lists 2711-19c16. when i try to download it goes to the checking terminal for compatability but gives me an error. Does anybody know if there is way to change this c16 or does it have to be that model. We do not have one like it.
The PV you have 2711-T9C8 has a DH+ port ( used to communicate with a PLC) and a AUX port (RS232 port) used to download/upload its programm or can be configured as a printer port. The AUX port (RS232 port ) cannot be used to communicate with a PLC. You have have to change the comm card or get a different PV with comms you need.
System comprising SLC 5/02 CPU. Panel View 900, 2711-T9A2. Ser E, Rev A, Frn 2.02. Fault: Panel view not transfering Command to move motors...
4,413
Greetings Everyone: I was having a problem with a PanelView 900 (Catalog # 2711T9C8) that I believe is not communicating with its associated SLC...
4,996
We have several PanelView 900s with RS232 and DeviceNet communication. We would like to be able to passthrough and download the panelview...
5,669
Hi, I'm trying to figure out how to properly update the "icons" on my Panelview 900 (AB 2711-T9C9). I think maybe I'm having a fundamental...
1,009
Panelview 900 communicates with SLC 5/03 PLC. When I upload the program from the panel, some buttons have the address B3/306, B3/304 etc. However...
2,457