PanelView alarms not displaying on Main Screen

macese

Member
Join Date
Mar 2017
Location
Hamilton
Posts
17
Hi,

I recently uploaded a project from the HMI to FT View Studio ME to make a few changes since I didn't have the original project. Once I restored the runtime application I was able to make the changes and download the new version to the PanelView Plus 1000 (using version 8.00).

The problem is now my alarm messages won't display on the main screen alarm banner. The alarms are still being shown on the alarm menu and other pages in the alarm banner but just not the main screen. I suspect this is an easy setting to fix but I'm not sure what to change.

Has anyone seen this before or knows how to fix it??
 
Are you filtering the alarm banner on the main screen? If so you will need to add new alarm triggers to display. Right click on the Alarm Banner > properties>Alarm Tab. At the bottom of the property page you will see a line identified as Filtering >Filter Triggers.
 

Similar Topics

I'm working on a project where the customer has specified I must use the HMI tag database for my HMI tags and not reference directly to the tag in...
Replies
5
Views
3,869
I am using a Micrologix 1400 talking to a Panelview Plus 400 with firmware 5.10 and using FactoryTalk View Studio - Machine Edition. When one...
Replies
0
Views
3,623
Hello all, Anyone knows is it posibble to "print" tag value on alarm message and how to do it? I want to create changes-log screen with...
Replies
2
Views
1,115
I have a system using a Panelview Plus Standard (2711P-T10C21D8S). It is configured with 86 alarms, most of which work fine, but for about five...
Replies
3
Views
2,251
Hello everyone, I have to program a PanelView plus connected to a Compact Guardlogix controller. The client has specified that there should be an...
Replies
3
Views
3,154
Back
Top Bottom