PanelView ETH with SLC500 5/04 via DH+/RIO backplane

tecnorads

Member
Join Date
Jan 2009
Location
flilpos
Posts
3
Hello
I have a configuration of two SLC500 5/04 in DH+ network connected to a card DH+/RIO in a backplane contrologix according to image.
http://img41.imageshack.us/img41/1253/slide1gzc.th.jpg
By configuring through the factotytalkview SE/ME 6.10, I include an RSLinx Enterprise Server.
The problem is that when browsing the root, the DH + network nodes do not appear. When I click "+", nodes are not shown. When I use the 1756-CNB, the ControlNet network nodes are shown. The problem is that the CPUs are in the SLC500 DH + network.
http://img6.imageshack.us/img6/3286/ftvd.jpg
How to create tags?
Sorry my english google.
:confused:
 
RSLinx Enterprise cannot browse through a 1756-DHRIO module to the DH+ network.

RSLinx Classic can. If you have RSLinx Classic OEM or Gateway, you can use it as an OPC Server for FactoryTalk View SE.
 
OK. There is no other way? This way I would have to keep your PC with RSLinx always connected to the PanelView work. Or not?
 
I was focusing on your description of FactoryTalk View on the PC and overlooked the title in which you mentioned PanelView.

You can connect directly to a DH+ network with RSLinx Enterprise using a 1784-PKTX card (on a PC) or a 2711P-RN6 module (in a PanelView Plus).

RSLinx Enterprise cannot bridge from a CIP network (EtherNet/IP and ControlNet) to a DH+ network. This is true for both the PC-based and PanelView-based runtimes of RSLinx Enterprise.

For a PC-based FactoryTalk View system, RSLinx Classic may be substituted to perform this routing.
 

Similar Topics

I have been working on this for a while now and I can't seem to get it. I was finally able to view the 1500 on the PanelView under the serial...
Replies
1
Views
99
Hi Everyone, Currently we have three plants running with Controllogix PLCs (L72, L73, L74). In each of these plants we have 2 FTView SE...
Replies
0
Views
67
Hey all, i have a panelview screen (image attached), with 4 items on it. Program 1, Program 2, ...3, ...4. The PLC i am using is a compactlogix...
Replies
5
Views
196
Hello All! Ok, we got a Work cell from a Integrator that is sending saved scanning data from the PLC to HMI (Panel View Plus) when I look at this...
Replies
3
Views
96
saludos a toda la comunidad Hace unos días he venido presentando pérdida de comunicación en una terminal hmi, anexo las imagenes de la secencia...
Replies
1
Views
113
Back
Top Bottom