Panelview Plus 1000 and SLC 5/03

getsmart

Member
Join Date
Nov 2014
Location
Cambridge, Ontario
Posts
5
Hi,

What configuration needs to be done in RSLINX ENTERPRISE RUNTIME in order that panelview plus 1000 to talk with SLC 5/03 ? I tried to copy the LOCAL one (which is seeing the slc) also configured again the DF1, but did not work ???
 
If you have copied the design to the runtime you will need to recreate the MER file and download that to the panelview.

There is a tick box when creating the MER file that says replace communications or something like that. Make sure that box is ticked along with run project at startup.

Cheers

Mark
 
As I mentioned in your other similar thread, the COM port number is described in the RSLinx Enterprise configuration for the DF1 Full Duplex driver.

If your USB/RS232 converter is set up to be COM3 on your development computer and you copy the Local schema to the Target schema, the COM3 port number will be copied as well.

On the PanelView Plus, the serial port is always COM1. If it gets a communications configuration telling it to use COM3, it can't run that driver.

So if you copy the Local schema to the Target schema, go into the driver configuration and change the COM port to COM1 on the Target side.

The advice to be sure you replace the existing communications configuration is also good advice.
 

Similar Topics

Hello, I made a change in alarm setup in factory view studio, where I changed a alarm message text. After that I made a run application and...
Replies
0
Views
140
Hi everyone, I've been tasked with creating a basic HMI for commissioning purposes for two pumps on a AB Panelview Plus 1000, 2711PRDT10C. I have...
Replies
16
Views
2,907
im tring to find out if i have a bad power supply for my panelview 1000 plus. does anyone have the pinout for the 10 pin connector on the...
Replies
1
Views
1,864
I need an X/Y plot to visually represent data o a roundness gage I am designing. ActiveX ME Chart Control UDT seems broke. Any advise one how to...
Replies
0
Views
665
Hello Everyone, I hope we are all good today! I have a project from 2015, and the customer is locked out of the HMI. They do not know what the...
Replies
5
Views
1,978
Back
Top Bottom