How to communicate between two PanelView 1000 and a SLC 5/04 on RIO network.
I have a SLC 5/04 and two PanelViews 1000. I want to show same project on two screen. For i do this, Should I add another I/O for each screen. or can i use same I/O for two panelview terminals.
For example, Two Input energized same Output in PLC.
I1:0 (Conveyor5 Start) for panelview 1
I1:1 (Conveyor5 Start) for panelview 2
OR,
Can I use same I/O in two panelview program.
If can i use it. how can i do it?
Sorry my english.
Please post the part number of your panelviews.
If they are for RIO communications, then they'll need to have unique addresses. It would be best to keep them separate anyway, even if they're on DH+.
You can simply parallel the logic in the PLC to send the same status information to each PV...
So, i must use another rack or group . is it true?
Yes, you will also need a 1747-SN module ( Remote I/O module)
to support your remote I/O connection.
Post the complete catalog number of your PV as requested above for the most accurate answers.
it is at my work. i can write tomorrow my PV catalog number.
Thanks for reply..
My company currently has 2 PV1000's. To be more exatct CAT# 2711-T10G8. FRN 4.46. I have experince with the AB products as far as the plc's. Can...
2,073
Hello all, I have a question I hope someone can help with. I have boxes (a literal pallet of boxes) with old panelview 550, 600, 1000, etc. I am...
26
927
I have an application where I will be using two PanelView Plus 7s to run two machines that share a common processor. The machines are identical...
407
Can a Panelview Plus 1000 replace a Panelview? If so how? So far the Panelview Plus 1000 doesnt see the file from the Panelview. Thank You.
1,190
Hi! Small question. I have a customer currently that is reporting an issue of 2 different panelviews running the same application connecting to...
2,305