Don't trust the system periodic function in RSView - I have discovered bugs in it when you are updating even a pretty modest amount of tags.
In general, if you need to execute an event 4 times a second then you are better off pushing that functionality into the PLC rather than struggling to do it in the HMI or SCADA. What exactly is it that you are trying to do? Some general advice as well - include what you are trying to do as well as the means you are currently having trouble with, since it helps people suggest alternatives.
Just adding a rotation to some images, i cant use the plc because it is only reading data from the controller every 1 sec. I seem to got it working, but id rather do it in the plc as well.
Create a new Derived Tag model executed at either 0.1 second or "Continuous". Create a memory tag (MyTag)and make it's equation
If (MyTag < 1000) then (MyTag +1) else 0
and you'll have a tag that sawtooths; that should be fine for adding rotation animation.
I would definitely avoid using a periodic event to trigger the sort of animation you are proposing. Remember that each event will normally be recorded in the activity log so four events a second (even if that is possible) will result in a vast amount of recorded data in a very short time.
Hi everyone, I'm Lelis and i have to make an event run every like 5-10 minutes. The action is: AppStart "C:\Folhas de Marcha\Fonte - Folha de...
1,500
I am new in programming. There are two things I am wondering about 1- if we set RPI of a module 20ms and if the scan time is for example 70ms...
2,430
Have you ever implemented an event driven periodic task in CLX? How'd you go about it? I have a task that needs to be executed at least every...
2,496
Hi, I'm new to RSView32. Does RSView32 has event and periodic event? Where in certain period an event will be trigerred automatically (Periodic...
4,838
Curios on the thoughts of using Continuous vs Periodic tasks. . The old SLC-500's mostly only had Continuous tasks. . The Compact & Control...
49
13,865