I have set up a 755 with dual encoder board to follow a filler drive motor position on a bottle filler and capper machine. The master encoder is mounted to the motor shroud of the filler. The slave encoder is mounted to the shroud of the capper. The 755 drives the slave (capper).
I used RA technote QA13283 as a template in setting up. I have everything running now, but the capper is gradually drifting out of time and has to be corrected by using an HMI button I added that momentarily adds an integer to the position offset velocity parameter in the vfd through a datalink.
If the capper drive is strictly following the position of the master encoder now, what should I be looking for as a cause? Would have to be a mechanical slop issue or could it still be a VFD setting issue? Many thanks
Ok, looks like we will be changing gearboxes then. The one on the filler has no part# or nameplate, all totally worn off long ago. I was entering my gear ratio based on the part # spec’d in the 25 year old drawings…
For anyone that may randomly be attempting a similar feat in the future, the solution for me was to avoid rounding the EGR numerator/denominator equations as much as possible (pf755 allows 6 places). That’s param 816 and 817. I had originally rounded to two places and apparently it was not giving the drive the granularity it needed to maintain accuracy.
Hi, I am having issues matching a 50HP submersible pump w/ a PF755 VFD (480V 3-Phase, 65(ND)/52(HD)). The failures occur at the static...
987
I have a relatively small network but I am having some issues with PowerFlex 755 drives (using the native ethernet card) Faulting with the F926...
214
I am having some trouble understanding what the break frequency is on a pf755. This is set in parameter 63. Rockwells description reads like the...
791
We have a Powerflex 755 set up for motion control that is giving us a overtemperature alarm. We swapped out the drive for one of our new spares...
2,107
Any chance any one has a list of all of the plant pax tags for a P_PF755 AOI in excel? I tried exporting all of my tags but only got the tag...
914