I want to develop a logic for a control valve. So i am using PID instruction in ladder logic, but i am not getting any output (%).
Can anybody send me a PID settings. So that i can check my ladder program.
Regards,
Manasee
PID ladder logic
Thanks for your valuable replies :)
Here i am attaching my ladder logic for PID controller. Pls advise / suggest on the faults in pid instruction setting if any.
Regards
Manasi
Greetings Manasee ...
I'm sorry but I only have a few seconds available to look over your program ... if I have more time soon I'll try to take another look ...
in the meantime I suggest that you double-check the settings on the PID's "Scaling" tab ... the values that you have there are not typical for a CompactLogix system ...
also, please read up on how the PID rung should be conditioned with a "False-to-True" transition to "trigger" the PID into executing at a specific time interval ... (coordinate this with the "Loop Update Time" setting ... from what I have had time to dig into so far, your PID rung appears to be constantly true (except for that XIO instruction) ... another (possibly better) "triggering" approach is to put the PID on an unconditional rung within a Periodic Task ... by improperly executing it on every scan (as apparently you are) both your Integral and Derivative actions will be GROSSLY out of adjustment ...
the XIO for the .MO bit should be removed ... putting the PID into (or out of) automatic mode should not be done by disabling the PID ... basic idea: let it continue to execute - but set the internal control bits (ex: .MO) to set the desired mode ...
I hope this helps ... I wish I had more time - but I'm swamped right now ... I'm sure that the other forum members will be able to help with your project ...
Hey folks, I was looking through some previous logic that I wrote and I have a question about a PID instruction. I did many of these for some air...
2,262
Folks, I would like to get some ideas/suggestions on how to use PIDE/P_PIDE in best way for my H&V system. I have one feedback: Temperature...
22
5,612
In control logix I have come across a few programs where the PID is setup in 1/sec, but most are 1/min. Where would this configuration be and when...
1,363
Hey guys, I'm taking a look at some existing code that I've converted from 90-30 to RX3i. I'm trying to figure out the configuration of some PID...
5,891
So over the last 6 months or so I put together a chiller system for the presses at our facility. some of them use in-die cooling. I am...
2,281