PID, PIDE and P_PIDE
See TN 672547, PIDE to P_PIDE Tag Mapping Table. Need either pcmd_man or ocmd_man in PIDE.
Also see the PDF, Enhanced PID PIDE.pdf,
in the file upload/download area (http://www.plcs.net/downloads/index.php?&direction=0&order=&directory=Allen_Bradley).
(Apologies if this is what jkerekes was referring to).
Suffice it to say, there is no one direct equivalent of the .MO bit.
(This block is powerful and versatile but seems needlessly complicated and 'feature-rich', especially concerning operating modes; it was probably designed by an oversized committee).
No the TN I was referring to outlines the mapping between the PIDE and the Plant PAx P_PIDE instructions.
It would seem the PIDE has no MO bit either
So based on the information below, anyone can help on what
I would do using the P_PIDE
.MO station mode (0=automatic; 1=manual)
.SWM software mode (0=no-auto); 1=yes- sw manual)
Software manual (.SWM)
This mode is also known as set output mode and allows the user to set the output % from the software.
The set output (.SO) value is used as the output of the loop.
The set output value typically comes from an operator input from an operator interface device.
Manual (.MO)
This mode takes the tieback value, as an input,
and adjusts its internal variables to generate the same value at the output The tieback input to the PID instruction is scaled to 0-100% according to the values of .MINTIE and .MAXTIE and is used as the output of the loop.
The tieback input typically comes from the output of a hardware hand/auto station that is bypassing the output from the controller.
Important: Manual mode overrides software manual mode if both mode bits are set on.
maybe a chase of the wild goose - but
I don't know ANYTHING about PAX - but maybe the class notes that I have posted on my website would be helpful - at least for the PIDE part ...
from my website menu - Sample Lessons and Videos - scroll down to the PDF file for PIDE States, Modes, Signal Flow ...
as I said, I developed these to be used as classroom notes/handouts - but you should be able to figure out what's going on - or ask questions if not ...
I have a PID instruction in the ladder logic with tag name pid1 I was trying to follow the youtube to create the PIDE faceplate, however, the...
1,188
In control logix I have come across a few programs where the PID is setup in 1/sec, but most are 1/min. Where would this configuration be and when...
1,366
Hi everyone, I have a project start up coming up in the next few weeks that I have 4 PID routines in my program. I have never used PID in a...
3,888
Hi, I am working on control level project using PLC 1756-L62 (Rockwell). I put the same parameters on a MATLAB PID and PIDE of Logix5000...
1,652
the following question was asked in a recent thread ... since the same question comes up quite often in my classes, I've put together a...
27
72,300