It would seem the PIDE has no MO bit either
So based on the information below, anyone can help on what
I would do using the P_PIDE
Thanks
.MO station mode (0=automatic; 1=manual)
.SWM software mode (0=no-auto); 1=yes- sw manual)
Software manual (.SWM)
This mode is also known as set output mode and allows the user to set the output % from the software.
The set output (.SO) value is used as the output of the loop.
The set output value typically comes from an operator input from an operator interface device.
Manual (.MO)
This mode takes the tieback value, as an input,
and adjusts its internal variables to generate the same value at the output The tieback input to the PID instruction is scaled to 0-100% according to the values of .MINTIE and .MAXTIE and is used as the output of the loop.
The tieback input typically comes from the output of a hardware hand/auto station that is bypassing the output from the controller.
Important: Manual mode overrides software manual mode if both mode bits are set on.