I'm new to using RSLogix5000. I want to set up a PID in ladder logic, but the setpoint field is read only. How do I give it a setpoint?

The application is: I have a 1769 L33 commanding a VFD/motor to put tension on a web for an unwinder. There is a load cell measuring tension on the web. So, if I understand this right, the tension feedback is my process variable, the commanded torque is my control variable, and I would like to put a calculated value into the setpoint, so that it will adjust torque to keep tension at the setpoint.

Thanks in advance,
Zac Slade
 
Oh, is that all?

Typically these instructions seem to have their most important components on the block itself. On this ladder logic block it only has an indicator for the setpoint, so I made an inaccurate assumption. šŸ™ƒ

Thanks for the help!
 
The VFD is a PowerFlex 755, and i'll have the PLC conrtolling it via Ethernet.

The VFD will be set to torque mode, so the PLC will use the Reference output tag in the PF755 hardware profile to set the torque. The PLC can ramp the motor up or down, as I program it to, by changing the reference tag.
 

Similar Topics

Hi All, I'm using Studio 5000 ver 30 to modify existing logic that has PID, and I want to be able to use an external/remote source as a setpoint...
Replies
3
Views
639
Hi all, I am having some difficulties with PID controllers, in particular writing the set point via HMI. I am using RSLogix 500, CCW and I have a...
Replies
8
Views
2,507
Hi all, Came across some examples today of PID instructions in an SLC 5/04 with the Setpoint (SMax) & Setpoint (SMin) both set to zero. In...
Replies
2
Views
1,953
I have a PIDE set up for controlling a tank level. I've run the autotune on it and it is working fairly well except for one thing. No matter...
Replies
4
Views
2,293
Any suggestions on an affordable temp pid controller with the option for remote set point? Thanks
Replies
2
Views
2,211
Back
Top Bottom