PID Single Loop Controller Vs. PLC
What are the pro's and con's of doing a psi or temp control pid loop in the processor vs a single loop controller?
Which method is best?
In the PLC you can alter parameters based on what is happening in the process.
In some processes, such as sterilization of an HTST , differential level control loops in a flash chamber have different parameters for startup, cooldown and process.
Based on what the program is doing, parameters can be altered or the PID put in Manual Mode all under program control without an operator.
Advantage of stand alone PID controllers, the Auto Tune feature usually works.
Advantages
Kid,
There are advantages to both, and that really is why there are both. Typically the need for the autotune isn't required in the PLC, because the PLC controls the whole process, and at time the desired response from the loop controller is specific to the process. I've personally never used the autotune on the PIDE. Usually, if anything, I've seen PLC PIDs tuned to be overdamped, due to other conditions that made the overdamped response from the PID ideal for the process.
Russ
hello.. I use S-315 to run plastic Extruder. There is heating zone with cooling fan to stabilize the temperature I have not found PID SIMO...
5,699
82
Hello, I have a motor that we are sending a RPM Speed Output from 0-100% to the VFD. However, the Motor HP needs to be limited to 6000 HP and the...
91
I have S7 1512C controler for controlling 48 PID temperature loop, the output is PWM. Please I need the best, most efficient way to write the...
608
Hi all, I'm having trouble solving a problem I've been working on for several months, and thought you might like a stab at it. The machine runs...
22
956