Pilz
ben
Jun 2002
37
Hello All,
Sorry but not really a PLC question…..
How do I link two Pilz relays (preferably PNZ0/1) that are 200m apart in separate MCC’s? I need e’stops at each location to trip both relays, and relay re-sets on each MCC panel front via reset button. Pilz have not been very good at responding. I could do with a drawing, the Pilz website is not so good either.
Thanks if you can help, or you have done something similar with PILZ?
Ben
How you describe it, it should be two separate E-stop relays. Each with its own E-stop and reset button. Both E-stop relays can stop the same machine/device.
It is quite normal to have several safety relays for the same machine.
I do NOT think that a reset button can be 200 m away from the E-stop button that was pressed. You have to be able to SEE the area that is relevant to that button. So you cannot share that function between the locations.
totally agree
that's right, you cannot have a non-local reset button. it would be easy to have either e-stop drop out both pilz relays (extra contact on the button maybe,connected to the other circuit) but (n)
to having either reset button bringing both back in.
totally agree
(whoops, login timed out:oops: )
Hi Guys, I'm trying to integrate Pilz Ethernet IP Module to ControlLogix. I added Pilz module as a Generic Ethernet module and I'm able to...
525
Long shot, anyone got the Pilz PDIA 2 Step 7 drivers zip file they could send me?
1,192
Dear All. I need comm between Compactlogix/Controllogix with PNOZ m1p ETH. What we need the communication option? or can be connect direct? many...
1,189
Hi Guys, First post here! I'll be working with PILZ Safety in a few weeks time, it will be communcating with Allen bradley, Studio 5000. I...
2,865
Hi guys, how to do connect "Pilz 772138" on hardware like the pic? is it possible? I am newbie on Siemens. Thanks
2,330