Piping Question
Tim Ganz
Dec 2010
Dallas, Texas
700
We have a system that has 1 inch pipe though the whole circuit ( cooling water ) and the control valve body is 1 ½. This is the only circuit like this and all the rest are 1 inch pipe and 1 inch control valve.
The odd circuit cools a roll that is about 7 feet higher than the rest but I am thinking that this ½ larger control valve makes no difference since the piping is the same size but others say it does.
I thought GPM through a pipe was limited by the pipe diameter? If this is true would the smallest pipe in the system be the limiting factor?
It depends on the type of control valve you have. In some cases the control valve presents a fairly big restriction to the flow and is the limiting factor. Going to a larger valve will usually help the flow in those cases.
The valve size makes a difference. How much of a difference depends on the amount of head loss through the valve compared to the total head loss through the system. If the valves are installed in a piping system with long runs of pipe and a lot of fittings then the valve won't matter much. If the valve is in a very short piping system and represents most of the head loss then it makes a big difference.
As Mendonsy indicates the type of valve makes a big difference too. A full port ball valve offers little restriction. A globe valve can be a big restriction.
That's probably a ball or plug valve, but it still doesn't provide enough info to answer your question. Piping must be analyzed as a complete system - a single component may or may not be critical.
No all restriction need to be added up, and the height too, with a certain flowspeed the pipe will need a certain watercolumn to get this speed, a bent is for example 1/2 meter pipe, an elbow is 1 meter a 1" valve is 3 meter a 1.5"is 2 meter etc.
I have a question about transitioning from EMT conduit to a device. For example this device, 24VDC with PNP output, does not contain a NPT...
2,345
I need few tips, info or suggestion about this piping system which one more suitable, Or any advantage or disadvantage using this type of design...
1,754
hi, can anyone guide me on how to go with freeze protection on piping, is there any standard products available or that is something to be...
2,320
Greetings Again! I would like to create some "pretty" 3D-type process piping on a RSView32 Graphic. I attend to animate this piping with color...
2,123
I have a 120V relay, 120V DI card and a analog input. I was wanting to know if i could put a 24V DI and well as a 120V DI card on the same plc...
85