PL7 Pro and TSX Micro... Cant get outputs to work!

aqueousdan

Member
Join Date
Jan 2016
Location
uk
Posts
32
Can anyone with some experience with PL7 Pro and TSX micro PLCs have a think and see why I may not be able to turn on outputs, either actual or memory bits.

I've attached a screen shot of my program while I am connected to the PLC. I can switch the inputs fine but it doesn't allow the output to be made. what am I doing wrong??

2017-07-06 13_15_03-Telemacanique - PL7 Pro + Zelio 2 + Lexium CT - VMware Workstation 12 Player.jpg
 
it is SR0 (subroutine).

You need first call subroutine to work (with coil)