plc 115vac input

rick62

Lifetime Supporting Member
Join Date
Jul 2013
Location
tuscumbia al
Posts
45
I keep losing this input on an dl06 automation direct plc, all inputs are 115vac, all of the other ones are ok, just one that I have had to move twice to another input- what is the best way to protect your 115 vac inputs from failing.
 
I keep losing this input on an dl06 automation direct plc, all inputs are 115vac, all of the other ones are ok, just one that I have had to move twice to another input- what is the best way to protect your 115 vac inputs from failing.

What is that input coming from? Can the device you're monitoring create an inductive spike when it turns off? Can you use an interposing relay on that input?

A properly rated MOV in parallel with the input, and connected to ground may help.

-rpoet
 
Since we're talking about it, can anyone recommend a MOV or snubber they'd recommend to put across the coils?

I tried picking one out on Mouser a few weeks ago, but all the choices are overwhelming.
 

Similar Topics

HI everyone, i am new to Siemens plc programming and i am in need of some help. yesterday we had an S7-1200 CPU 1214C fail to turn on an output to...
Replies
3
Views
52
Hello, I have a Mitsubishi FX3G 14M PLC and a E615 HMI from Mitsubishi/Beijer. I'm using GXWorks 2 to do the programming and I have no problem...
Replies
3
Views
53
Hi, I'm trying to import a Rockwell/AB EDS to Beckhoff but I'm not sure how to import/install the EDS. It is a PowerFlex 525 EDS. Is there a way...
Replies
1
Views
75
I want to communicate my Q series PLC with Factory IO using GX works 2 software, I want to use modbus as server and the ips are as follows plc...
Replies
0
Views
50
Hi everyone. I'm trying to read values from a Loadcell with a 2080-TC card. I know the 2080-TC is a thermocouple card but it reads millivolts that...
Replies
4
Views
88
Back
Top Bottom