A question was sent via PM this morning from a new member (Vince9521, from up in Timmins, Ontario) that I'm promoting to the main forum:

plc-5 1771-DA,
I am trying to set up the card but from what I read I need to initialize the card but am i able to do that with out the special programmer. Or can I initialize it with the processor and data files ?
 
Last edited:
The 1771-DA was an ASCII communications module from the early 1980's that was used with PLC-2, PLC-3, and PLC-5 Classic controllers. With the advent of the Channel 0 serial port on the PLC-5 Enhanced and the more capable 1771-DB BASIC52 interpreter module, the 1771-DA declined in popularity.

My recollection is that it was configured and controlled entirely by ladder logic and Block Transfer instructions. I don't think there is a "terminal mode" or menu-driven configuration function.

The User manual is available from the RA Literature Library, but because of its age the step-by-step instructions focus on the PLC-2 and PLC-3.

https://literature.rockwellautomation.com/idc/groups/literature/documents/um/1771-um513_-en-p.pdf

What is your goal: are you trying to repair or troubleshoot an existing system, or are you trying to program one of these modules to add features to a PLC-5 system ?

Post as much context and detail as you can about your processor (model of PLC-5) and application (what's connected to the RS-232 port ?).

And again, welcome to the PLCTalk forum community !
 

Similar Topics

Hey everyone, Trying to bench test the I/O on a program that I converted from a PLC-5 processor to a ControlLogix processor but still using the...
Replies
21
Views
6,520
I am doing a little self training and looking for some feedback. I have a plc 5 with a 1771-il module looking into some scaling issues with an...
Replies
1
Views
1,396
Hi, We have a customer using PLC-5 system with RIO. From what they complain is the slow speed of the PLC DI (normal), thus they wanted to get...
Replies
17
Views
10,452
These two RTD's are wired to channels 1 and 2 on a 1771-IR in a remote rack, communicating to a PLC-5/40 through an ASB. I believe that the RTD's...
Replies
7
Views
1,966
Hello, I am in the process of migrating a PLC-5 system over to ControlLogix and could not find any equivalent modules to convert the 1771-ALX...
Replies
2
Views
1,490
Back
Top Bottom