PLC 5 1771 - IFE Trouble
Silver72
Feb 2011
Alberta
Hi, currently have an series A IFE module in PLC 5 chassis. Running fine for years. Last week starting getting erratic data from all channels (only using 3 channels). Swapped card, power supply nothing works. Funny thing is, if only 1 channel hooked up data is correct for that channel, when hooking another channel up, all data starts to go erratic? Nothing has changed in our process.
The new card you put in, is it a series "A"? Did you check all the jumpers on the new card to match the old?
Yes, I made sure all switches are correct. Don't think it's a card problem, both new and old cards act the same. Could it be a backplane problem? Noise? Interference from another card?
Short answer, yes. Do you have a way to test the cards in another system or test chassis? Thus eliminating the cards as the problem.
Our production process is 24 hours a day. Only time is on weekend, which I plan to do more testing. Would appreciate any more ideas which I could try now or when production stops for the weekend. I will move card to another chassis to see if problem follows.
Thanks again.
If you are using differential analog inputs your problem is more difficult than using single ended inputs
Try to avoid mixing voltage and current signals on the same card unless you can tie the commons very tightly to one end of the same power supply
In fact the only analog inputs that I have difficulty with are differential inputs that cannot, and never will work as single ended inputs, boss won't buy isolators for each channel so I live with the noise and try to develop methods to minimise it
try reading you may need a tech connect contract to sign in to see this one
http://rockwellautomation.custhelp.com/app/answers/detail/a_id/14088/kw/1771 ife noise/r_id/113025
Try reading this manual
Chapter 7
http://literature.rockwellautomation.com/idc/groups/literature/documents/um/1771-um663_-en-p.pdf
Urgent!! Hi all I am a newbie here. Currently I am migrating from plc-5 to controlLogix. When 1771-IFE change to 1756-IF16, I am getting a...
2,385
My question is, when there is 10V on the first channel of an 1771-IFE card, what decimal value will show up in the data file word (happens to be...
6,094
I have a tonnage monitor module hooked up to an analog card using a plc 5-30. Analog Card is a 1771 IFE/C. We had the OEM visit to do calibration...
1,747
I need to add an analog input to this legacy plc 2/17 system. I placed the module in the very last slot of an 8 slot chassi, next to an on board...
1,928
Guys, I am having problems setting up an analog in module. The PLC is existing, and has two 16 slot chassis. Single slot addressing. My new module...
3,110