PLC 5/25 with PLC5/60 as Backup?
PIPHVAC
Oct 2011
NS
Hello,
I have a redundant system in which there are 2 x PLC 5/25E's configured with each other and both share the same RIO rack.
However one of the PLC 5/25E processors faulted and somebody has replaced it with a PLC 5/60 (un-programmed).
Is it simply a case of uploading the program from the master plc 5/25e, editing it to use the PLC 5/60 processor, then downloading it to the PLC 5/60 module?
Regards,
John
You had?
Who did this and why did they leave it that way?
Have you done this part if so can you post the file? If not do you have the software to do so? Do you have any documentation and/or a copy of the original program and configuration?
Have you up-loaded from the processor and can you post that file?
What was the fault?
Do you have a list of rev#s, part#s and can you post them?
Best regards, Steve
I don't think there was a requirement for both PLCs to be the same model or even the same generation, with the old PLC-5 Hot Back up system. All the interfacing with the 1771-BCM modules was done with ordinary Block Transfers.
It certainly made sense to have both controllers be the same; you'd have the same memory footprint and execution speed and firmware functionality, and they'd appear the same to a DH+ network when you swapped between them.
It can't hurt to try.
I can confirm that it does work as ive done it before. :p Just make sure to set all the dip switches the same for the DH+ and RIO ports, as you would if you were replacing like for like.
When downloading to the PLC it will probably come up saying processor type doesnt match what is selected in RSLogix5. Just press ok and it SHOULD change it to your 5/60.
I am getting ''Bad system configuration'' fault from the Plc5 processor maybe three times a week or less or more. After getting clear this error...
2,764
Hello All, I am replacing a Panelview 1400E with a Panelview Plus on a system with a PLC5-30 processor. I have most everything worked out with the...
2,632
I'm bidding on a project to upgrade a machine that is using a PLC5/30 and a PC based user interface that is running on Windows 3.1. The...
35
9,796
I have a customer with an old machine run by a PLC5 that I put an ethernet sidecar on in 2005 for a panelview. We are looking at integrating it...
2,027
HI GUYS; I discuss some issu and want possible solutions. please help me The issu is that we have gas turbine from solar commision in 1994 which...
2,795