PLC 5/80 and Controllogix L64 comm setup on DH+
amitpowar
Apr 2013
Pune
I have a Controllogix L64 and PLC 5/60.
I want to fetch data from CLX to PLC -5 and vice versa.
CLX rack has a 1756 - DHRIO card.
Since this is simulation setup I only have two devices on DH+. I have termination resistor on either ends.
Node ID on PLC 5 channel 1A is 7 and Link ID is 21
Node ID on CLX channel A is 4 and Link ID is 15.
DH+ Status Indicators on Both sides are Green Blinking. Which as per the manual means there no other nodes present on network.
I checked the cable conductivity and found OK.
I do not know if anything else needs to be configured.
Please help me troubleshoot.
Thanks in advance.
Be sure that both devices are set for the same data rate; 57.6 kb/s or 230.4 kb/s.
Check to be sure the blue and white wires are on the appropriately numbered terminals; you want Terminal 1 connected to Terminal 1, and Terminal 2 connected to Terminal 2.
The Link ID values will not matter for local DH+ messaging.
I have a Controllogix L64 and PLC 5/60. I want to fetch data from CLX to PLC -5 and vice versa. CLX rack has a 1756 - DHRIO card. Since this is...
2,507
76
Hi everyone i have a customer, who wants to show an alarm on the machine, if the I/O forces are enabled and set, on at ControlLogix L81E with...
271
Hi Everyone, I am currently trying to communicate ControlLogix PLCs via EtherNet/IP with Delta V DCS. There is a VIM2 card configured for...
301
Hello everyone, been trying to figure this one out for awhile now. The system configuration is as follows: Processor is an L63 5563 ControlLogix...
618
