TimWilborne Lifetime Supporting Member Join Date Oct 2005 Location Roanoke, VA Posts 2,210 Jul 29, 2008 #16 Post your program real quick. You've got about 2 minutes before I walk out the door
Gunther Garland Member OP G Join Date Jul 2008 Location NL Posts 19 Jul 29, 2008 #17 The 24VDC is the problem. Thank you for your help.
TimWilborne Lifetime Supporting Member Join Date Oct 2005 Location Roanoke, VA Posts 2,210 Jul 29, 2008 #18 Cool, good luck with you project
Gunther Garland Member OP G Join Date Jul 2008 Location NL Posts 19 Jul 29, 2008 #19 Turns out, the 24VDC is not the problem. We are using the internal power supply. There is still no signal from the analog output. Any advice would be greatly appreciated.
Turns out, the 24VDC is not the problem. We are using the internal power supply. There is still no signal from the analog output. Any advice would be greatly appreciated.
Gunther Garland Member OP G Join Date Jul 2008 Location NL Posts 19 Jul 29, 2008 #20 We are now getting a signal, however it is half the value. We are placing a 4-20mA signal using a fluke meter. We believe that it is because of the progam or fault value(s) but we are not sure what values to change them to.
We are now getting a signal, however it is half the value. We are placing a 4-20mA signal using a fluke meter. We believe that it is because of the progam or fault value(s) but we are not sure what values to change them to.
jimbo3123 Member J Join Date Sep 2003 Location Detroit Area Posts 550 Jul 29, 2008 #21 Gunther Garland said: We are now getting a signal, however it is half the value. We are placing a 4-20mA signal using a fluke meter. We believe that it is because of the progam or fault value(s) but we are not sure what values to change them to. Click to expand... You are getting a signal that half the value of what? If you are using 0 to 10V on your input card, and it is setup for raw/proportional, you should read a value of 0 to 31206 on the input data word. If you have the input setup for 4-20mA, raw/proportional, you should read a value range of 6241 to 31206 on the input data word. These all came from the manual that you can find here: http://literature.rockwellautomation.com/idc/groups/literature/documents/um/1769-um002_-en-p.pdf
Gunther Garland said: We are now getting a signal, however it is half the value. We are placing a 4-20mA signal using a fluke meter. We believe that it is because of the progam or fault value(s) but we are not sure what values to change them to. Click to expand... You are getting a signal that half the value of what? If you are using 0 to 10V on your input card, and it is setup for raw/proportional, you should read a value of 0 to 31206 on the input data word. If you have the input setup for 4-20mA, raw/proportional, you should read a value range of 6241 to 31206 on the input data word. These all came from the manual that you can find here: http://literature.rockwellautomation.com/idc/groups/literature/documents/um/1769-um002_-en-p.pdf