PLC controlling different devices

Shohadawy

Member
Join Date
Aug 2008
Location
Egypt
Posts
66
I know that the operation of the PLC is based on passing the driving electrical signal or not passing it according to the sequence of its program. If I'm connecting a 24vdc solenoid valve to a PLC and a 220 VAC motor to the same PLC what driving signal shall I apply to my PLC, 24vdc or 220vac?
 
Part of the idea of 'modular' PLCs is that the input and output signals do not all have to be the same voltage range. Manufacturers produce different modules to handle 24VDC, 110VAC, 220VAC etc...
So if you have two devices with different voltage requirements you use two modules: a 24VDC module and a 220VAC module. Wire each of these with the relevant 'driving' voltage and connect each one to its device. The PLC CPU simply switches an output on or off: the CPU doesn't really know or care whether the result of the operation controls 24VDC or 220VAC.
 
Shohadawy,
The voltage of your motor doesn't matter. What is the voltage of the coil of the motor starter? Request a 24vdc coil and then you can use the same output card to control both the solenoid and the motor starter (unless it's a large motor starter, then use an interposing relay between the output card and the motor starter).
 

Similar Topics

Hi All, I am facing one issue with the SEW MDX61B drive. Issue- I want to run a conveyor with this drive in two directions but it runs in...
Replies
0
Views
351
Hello. I am using the following: Eaton E4-AC-12RXP PLC I am trying to control the CL86T which controls a Closed-Loop Stepper motor. I am using...
Replies
3
Views
982
Hi all, I'm new to this forum and really new to the world of PLCs. This may seem like a really dumb question but is it possible for a HMI to...
Replies
6
Views
1,778
Hello everyone... I am new to the PLC world and I would really love it if you gave me some interest about the problem I am dealing with for about...
Replies
15
Views
4,088
Urgent Help needed I have to migrate a S7 300 PLC system controlling a plant which is currently in operation, from SIMATIC NET V6.3 to V.15...
Replies
0
Views
1,348
Back
Top Bottom