PLC or Modular controller for tank heating
JBauer
Dec 2012
Worcester
Hello,
I need to control the temperature and water level in a tank, opening valves to increase temperature or water if required. What are the differences in using A) Red Lion T1611100 B) Red Lion CSMSTRV2 C) CSMSTRSX or D) Mitsubishi PLC
Thank you very much for your help.
The RedLion T16xxx is a stand alone loop controller. Most single loopers will do either on/off control or PID control. It will certainly do PID control for tank temperature. but it won't do cascade control which is frequently used for jacketed vessels. It has its own interface, its own HMI, so the setpoint can be changed and the temperature displayed. Depending on what you use for level sensing, one of these will work if the sensor is continuous (4-20mA) but it will not work for discrete point level switches. But there are simple control modules that will do pump-up or pump-down that work with point level switches. Single loopers program from the front panel, software is not needed.
The Red Lion CSM is a modular controller. It is a PAC (Process Automation controller), more targeted at PID process control than fast (mS) discrete automation, a good fit for temperature and level control. It is a controller module, it needs a power supply and I/O modules, depending. An HMI display is needed for temperature/level display and to be able to change the setpoint. RedLion sells HMI displays, too. Software is needed for configuration. Last time I looked, Red Lion software for the HMI was free, I think it is for this unit, too.
The PLC is a PLC. You buy the needed I/O modules and program the PLC to do what's needed. PID control (as opposed to any on/off control) is quite common on PLCs nowadays. I don't know if any particular Mitsubishi model does PID. An HMI is needed for temperature/level display and to be able to change the setpoints, which needs its own programming. Software is needed to program the PLC and the HMI. Many PLC vendors charge for software.
For a newbie it is difficult to differentiate between these two types of PLCs. What I am able to understand that Modular PLC does have modules but...
6,899
Hi, can i please get some help with these types of plc's 🤞🏻 what is the Unitary plc, Modular plc and Rack-Mounted plc? and also if possible...
28
17,519
Hi all, I am very new to PLC's as a subject but am keen to learn! I am taking this subject at HNC/D level and have no previous knowledge on the...
6,870
We're using a lot of Allen Bradley IFM modules (Connecting to ControlLogix I/O cards) in our panels, and are considering replacing them with...
3,364
I'ld like to know about the Triple Redundant Modular PLC/DCS and the make and models with all the fundas.
3,384