PLC Orientation - Installation

Barneel

Member
Join Date
Aug 2013
Location
UK
Posts
18
A quick question - do compact/control logix PLCs have to be oriented in the upright position? I've been trawling through the manuals but haven't found anything that says they have to be, but I thought I'd ask the pro's.

I'm asking because for my current job it would be far more convenient (and I like convenient) to be able to install them so the back is facing the floor in the little space I have.


Thanks,
B
 
It will degrade natural cooling of the PLC.
Most PLC manuals I have seen says dont do it, or states a much decreased am bient temperature value, like 40°C instead of 55°C.
 