PLC Rung Scanning
ControlLogix
Feb 2003
Southern Ireland
62
Hi folks,
I am having a little trouble with a rung of code which appears at the bottom of the msg (Sorry, don't know how to paste it in here :( ). The tag called TmpInt is used to called a program within an Emerson servo drive. There is an offset of 4 within the Emerson setup so to call program 1, a value of 5 has to be actually sent to the Emerson. Therefore TmpInt will contain a value of 1, 4 is added to it and Emerson1.Seq.Function2 is latched.
Now TmpInt is calcualted via the 1st instruction (the CPT). Now all values for TmpInt will be in the range of -1 to 10...I know that for a fact since I worked through all possible values for all the variables. Now to my problem....
If I have a value of 1 in TmpInt after I do my CPT instruction, the LIM instruction will be true and therefore move a value of 9 into TmpInt. That now means however that program 13 will always be called regardless of the value of the calculated TmpInt...which should in theory call program 5 in my Emerson drive. Am I correct in what I am saying or is TmpInt recalulated prior to the Add instruction?
Any feedback on this would be much appreciated.
Regards,
A boggled mind!!
CPT(TmpInt,LowRamLevel-RamLowLimit)[LIM(10,TmpInt,-1)MOV(9,TmpInt)MOV(InsertionMgr.RamHighLimit,InsertionMgr.LowRamLevel),ADD(TmpInt,4,Emerson1.ProgNum)OTL(Emerson1.Seq.Function.2)];
LIM fun and games
Look again at your LIM instruction. I'll draw out the rung here:
+--------- LIM ---+ +-------- MOV ---+
---| LOW LIM: 10 |----| SOURCE: 9 |
| TEST: TmpInt | | DEST: TmpInt |
| HIGH LIM: -1 | +----------------+
What this code is saying is that if TmpInt is OUT OF RANGE of -1 to 10, move a 9 into it.
Notice that the HIGH value is -1 and the LOW value is 10. Normally you put the smaller number (-1) in the Low and the larger number (10) in the High. When you do it this way, it reverses the logic of the LIM instruction. The LIM solves TRUE if Test is GREATER than 10. It also solves TRUE if Test is LESS than -1. But because High is less than Low, it solves TRUE when you have only one condtion, not both.
It's a dirty trick, but very useful.
Allen,
Thanks for your reply. I knew that I was starring too long at the code to see an answer. A fresh pair of eyes made all the difference.
Thanks for your input,
Rgds,
A Crystal Clear Mind
I have often seen statements that arranging rungs so that the condition most likely to make the whole rung TRUE (or FALSE) should be placed to be...
29
8,653
I added a rung comment then which is associated to an OTE. I moved the comment to a different rung but the yellow "highlite" is still where the...
1,973
Recently had an issue that I tracked down to a frozen rung of logic. The PLC is an AB PLC5/40E. the rung of logic is simple. (I hope the text...
3,645
Not Sure why I can't implement this piece of PLC-5 logic in a Micrologix 1100 !!!!!! In Micrologix 1100, S:42 = RTC Seconds Register. I...
31
26,305
160