I am working on a conversion project to upgrade a machine's controller from a PLC2 to a CompactLogix. I know how the inputs and ouputs are addressed, however there are some output coils addressed as 030/0X and 031/0X. This would seem to indicate there is a rack 3, however there is only one physical rack. Is this an internal memory address? Other than that there are a bunch of 04X and 05X timer addresses.
Thanks in advance!
All the other responders are correct. Non-physical data table addresses can be used for programming, timers, etc. Totally legal, and, back-in-the-day, usually needed because of the small amount of memory.
However, with the information given, we can draw no conclusions.
JUST BECAUSE 04x and 05x are timers does NOT mean that there's not a rack 6 or higher actually in use.
DIP switches are the rule of the day on this, expecially with remote racks.
And, the BIT level addressing in a PLC-2 is, as you may know, OCTAL (no 8's, no 9's.
In your 030/ and 031/ reference, the '0' means output, the '3' means logical rack 3, the "0" or "1" means Module Group, and, the 0X would be the bit.