PLC4J/X and ControlLogix 5000
AndyPLC
Apr 2022
Pennsylvania
I'm attempting to read tags from a 1756L81E(FactoryTalk Logix Echo) controller using the PLC4J api. I have one read and one write bool setup in the controller tags set for external access of read/write and read only, respectively. Using the remote run, I can see/update the tags via Logix Designer. I can also connect to the PLC using the software I have, but when I go to read, I'm getting "Unsupported case for discriminated type" when I get the response.
PLC4J code below:
Code:
try (PlcConnection plcConnection = new PlcDriverManager().getConnection("eip://127.0.0.1")) {
	if (!plcConnection.getMetadata().canRead()) {
		logger.error("PLC connection doesn't support reading.");
		return;
	logger.info("PLC connector connected");
	// Create a new read request:
	PlcReadRequest.Builder builder = plcConnection.readRequestBuilder();
	logger.info("Created Builder");
	builder.addItem("value-1", "%Output_Tag[0]:BOOL:1");
	PlcReadRequest readRequest = builder.build();
	// Register a callback executed as soon as a response arrives.
	logger.info("Make sync request for PLC data");
	PlcReadResponse readResponse = readRequest.execute().get(5000, TimeUnit.MILLISECONDS);
	if (readResponse != null) {
		printPlcResponse(readResponse);
	} else {
		logger.error("An error reading PLC, response is NULL");
} catch (PlcConnectionException e) {
	e.printStackTrace();
Output in logs:
Code:
DEBUG o.a.plc4x.java.spi.Plc4xNettyWrapper - Forwarding request to plc CipRRData[sessionHandle=1073741845,status=0,senderContext={0,0,0,0,0,0,0,0},options=0,exchange=CipExchange[service=CipUnconnectedRequest[unconnectedService=CipReadRequest[RequestPathSize=7,tag={-111,10,79,117,116,112,117,116,95,84,97,103,40,0},elementNb=1],backPlane=0,slot=0]]]
DEBUG o.a.p.j.s.GeneratedDriverByteToMessageCodec - Sending bytes to PLC for message CipRRData[sessionHandle=1073741845,status=0,senderContext={0,0,0,0,0,0,0,0},options=0,exchange=CipExchange[service=CipUnconnectedRequest[unconnectedService=CipReadRequest[RequestPathSize=7,tag={-111,10,79,117,116,112,117,116,95,84,97,103,40,0},elementNb=1],backPlane=0,slot=0]]] as data 6f0030001500004000000000000000000000000000000000000000000000020000000000b2002000520220062401059d12004c07910a4f75747075745f5461672800010001000000
WARN  o.a.p.j.s.GeneratedDriverByteToMessageCodec - Error decoding package with content [6f0018001500004000000000000000000000000000000000000000000000020000000000b2000800d200010111030100]: Unsupported case for discriminated type
org.apache.plc4x.java.spi.generation.ParseException: Unsupported case for discriminated type
Any thoughts or Missing information from the post?
According to docs and examples I've seen, the first field is basically a key. The second is the information about what you are trying to read. The format for the second is:
Code:
^%(?<tag>[a-zA-Z_.0-9]+\\[?[0-9]*\\]?):?(?<dataType>[A-Z]*):?(?<elementNb>[0-9]*)
Perhaps I misread?
... it looks like it's trying to read 14? tags?
If you mean this:
Code:
That is not 14 tags, those are SINTs as ASCII codes*: 79=O; 117=u; 116=t; ...; 95=_; 84=T; 97=a; 103=g; 40=0 (the zero in [0]?); 0=string terminator, or perhaps the zero in [0]?
Maybe the [0] is not allowed? And the <elementNb> is where the array index should be, so Output_Tag[0] should be
Code:
builder.addItem("value-1", "%Output_Tag:BOOL:0");
? I am only guessing. Also, I would not use the hyphen in the key, so I would use "value_1" instead of "value-1" although it may not matter.
[update: whoops, I found a webpage page that suggests hyphens in the key for .addItem are legal; also [0] is the starting element]
8-bit ASCII -111 (145) is ETC (end transmission block) with thbit 7 set, and ASCII 10 is linefeed (newline), but I have no idea where they come from or what they mean.
* Not strict ASCII i.e. 8-bit not 7-bit, because the -111 at the beginning is presumably ASCII 145 (256-111)
Ok, plc4x adds those two chars in to meet the CIP message spec. The 0x91 is the data item id(although I couldn't find that item id in the spec) and the 0x0A is the length of the data. So now I suppose I need to see what else the controller may be complaining about.
But much thanks for the help getting rid of the last two chars in the tag!
Could you get a Wireshark trace? You would need a switch with mirroring port function. The Wireshark dissector for EtherNet/IP is great and decodes and comments the CIP package down to the guts of the packet. it may be easier to analyze than the logs you have shown.
Wow, yes it does! Since I'm running the 5000 emulator, I just had to sniff on the loopback. Gave me the error and one google away and I got it. Issue was with the options for the backplane and controller location in the connection string.
79
141
Why does the controllogix redundancy modules use a single mode fiber vs multimode fiber?
116
Hello, I have two 16 point input cards and 1 16 point output card showing module faulted on my IO tree in Logix Designer. The fault code is...
245
Hello, My associate and I are trying to sync up two ControlLogix racks (7-slot chassis) with identical modules. We are able to see the secondary...